HELLO
We have new pdus AP8886 with NMC3. When we connect its network port to cisco switch the link stay down and the light on the network port and on the switch are off. When i connect the PDU network direct to my pc computer the pc connect (web) to the PDU and all lights on PDU network card are on. I want to say that the new PDU is connected to switch port that now AP8886 with NMC 2 connect to it and work but when we connect the NMC 3 it does not work - there is no connect even on layer 1-2 the are off. We check the port switch and the PDU port By connect it to pc and to another PDU network port and it work but not when we connect it to the switch. I also upgrade the firmware of the PDU
WHY??? what can i chek ?
thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-04-02 02:23 AM
Problem solved. I upgrade the firmware and from serial port i change the port speed to auto and reboot the network card .
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-04 02:22 AM
Good morning
I have 4 displays (Version 0N-1642), I think these cards will be from V3.
At this moment the cards show nothing on the display, I think the Fw is corrupt or incorrect. Because it was done with the PEN of the “other NMCV2 cards….
1- Validate the correct version of these cards
2- What is the current firmware for these cards
3- How to update the fw on the cards (create apcfirm folder, place the firmware and the nmc3.rcf file inside)
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-04-02 02:23 AM
Problem solved. I upgrade the firmware and from serial port i change the port speed to auto and reboot the network card .
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-04 02:22 AM
Good morning
I have 4 displays (Version 0N-1642), I think these cards will be from V3.
At this moment the cards show nothing on the display, I think the Fw is corrupt or incorrect. Because it was done with the PEN of the “other NMCV2 cards….
1- Validate the correct version of these cards
2- What is the current firmware for these cards
3- How to update the fw on the cards (create apcfirm folder, place the firmware and the nmc3.rcf file inside)
Thanks