I have two ATS APC AP4424 Models which appear normally on DCE (all sensors work normally) but I get an error "Device Definition File (DDF) Transfer Failure " I have checked the Device File Transfer Settings' lists the Username, Password and IP Range combination needed to access this device and I have verified that the ftp service runs on the ATS devices (I am able to connect with a ftp client to the device)
(CID:140713749)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 05:58 PM . Last Modified: 2024-04-03 03:10 AM
Dear Interworks.Cloud,
Tell us, please, did you solve your problem or not?
With respect.
(CID:141269201)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 05:58 PM . Last Modified: 2024-04-03 03:10 AM
yes it worked with the firmware upgrade
(CID:143754906)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 05:58 PM . Last Modified: 2024-04-03 03:10 AM
Ok, very thanks for the good feedback 😀.
(CID:143754910)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 05:58 PM . Last Modified: 2023-10-20 04:56 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.