AP9631 Discovery

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • AP9631 Discovery
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
128
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 11:37 PM . Last Modified: ‎2024-04-03 12:04 AM

0 Likes
6
1280
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:37 PM . Last Modified: ‎2024-04-03 12:04 AM

AP9631 Discovery

Hello,  I just installed 2 APC SRT2200RMXLA with AP9631 NMC cards. I can access the cards through the web browser.  SNMP1 is enabled and SNMP3 is disabled on NMC. When I run discovery it doesn't find the UPS.  Never had this issue before. Any idea? Thanks 

(CID:152077536)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 11:37 PM . Last Modified: ‎2024-04-03 12:04 AM

0 Likes
4
1281
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:37 PM . Last Modified: ‎2024-04-03 12:04 AM

Hi Jan,

 

The following k-base should help with most discovery issues:

http://www.apc.com/us/en/faqs/FA177081

 

This one may be helpful for troublshooting SNMP issues:

http://www.apc.com/us/en/faqs/FA226273

Note that the last one seems more specific to lost com if the device is already discovered but many aspects are generic SNMP troubleshooting aids.

 

Thanks,

Steve

(CID:152077542)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 11:37 PM . Last Modified: ‎2024-04-03 12:04 AM

0 Likes
4
1282
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:37 PM . Last Modified: ‎2024-04-03 12:04 AM

Hi Jan,

 

The following k-base should help with most discovery issues:

http://www.apc.com/us/en/faqs/FA177081

 

This one may be helpful for troublshooting SNMP issues:

http://www.apc.com/us/en/faqs/FA226273

Note that the last one seems more specific to lost com if the device is already discovered but many aspects are generic SNMP troubleshooting aids.

 

Thanks,

Steve

(CID:152077542)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 11:37 PM . Last Modified: ‎2024-04-03 12:04 AM

In response to DCIM_Support
0 Likes
0
1281
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:37 PM . Last Modified: ‎2024-04-03 12:04 AM

Hi Steve,

yep the log did show "Detected an unauthorized user attempting to access the SNMP interface from". Do I need to change the access control on the NMC or in DCE? The NMC access controls shows the following:

(CID:152077569)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 11:38 PM . Last Modified: ‎2024-04-03 12:04 AM

In response to DCIM_Support
0 Likes
0
1281
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:38 PM . Last Modified: ‎2024-04-03 12:04 AM

Hi Jan,

 

If you're trying to discover via SNMP version 1 and these are your settings, it will not discover, You need to click into one of the links such as "Community Name 1" and set the community name that you're going to use in the SNMP version 1 discovery in DCE. You also need to set that one to "read".


Next, click another one of the links such as "Community Name 2" and set the community name that you're going to use in the priority scanning section in the SNMP version 1 discovery in DCE. You also need to set that one to write or write+.

Thanks,

Steve.

(CID:152077582)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 11:38 PM . Last Modified: ‎2024-04-03 12:04 AM

In response to DCIM_Support
0 Likes
0
1281
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:38 PM . Last Modified: ‎2024-04-03 12:04 AM

Hi Steve,

Never had to do that before, but got it, thanks for your help.

(CID:152077593)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 11:38 PM . Last Modified: ‎2024-04-03 12:04 AM

In response to DCIM_Support
0 Likes
0
1281
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:38 PM . Last Modified: ‎2024-04-03 12:04 AM

Hi Jan,

If the new cards are running 6.8 firmware, that's a new security feature...SNMP is disabled by default with no default community names. It does add an extra few steps so I'm not that fond of it but security conscious people will always win that argument.

 

Steve

(CID:152077596)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 11:38 PM . Last Modified: ‎2023-10-20 04:56 AM

0 Likes
0
1281
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 11:38 PM . Last Modified: ‎2023-10-20 04:56 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore