AP8853

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

DCIM_Support
Picard
Picard
0 Likes
2
179

AP8853

This question was originally posted on DCIM Support by Fabrizio Carioti on 2018-02-28


Hi,

is it possible monitor a Rack Pdu AP8853 via Modbus TCP directly on NMC ?

(CID:128761836)

2 Replies 2
DCIM_Support
Picard
Picard
0 Likes
0
179

Re: AP8853

This answer was originally posted on DCIM Support by Christopherus Laurentius on 2018-02-28


No, AP8853 does not support Modbus TCP directly.

It does support SNMP v1 or v3  protocol.

 

You will need to get converter to convert from SNMP v1 or v3 get to Modbus TCP.

There are a few of the shelves converter, you need to find one that is available locally.

 

Alternatively, if this AP8853 is monitored by DCE, you can use AP95MODBUS to get DCE to output AP8853's sensor via modbus TCP (up to 247 modbus slave ID per 1 DCE)

 

Regards,

Chris

(CID:128761886)

DCIM_Support
Picard
Picard
0 Likes
0
179

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.