EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:36 PM . Last Modified: 2024-04-05 02:35 AM
Hi,
is it possible monitor a Rack Pdu AP8853 via Modbus TCP directly on NMC ?
(CID:128761836)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:36 PM . Last Modified: 2024-04-05 02:35 AM
No, AP8853 does not support Modbus TCP directly.
It does support SNMP v1 or v3 protocol.
You will need to get converter to convert from SNMP v1 or v3 get to Modbus TCP.
There are a few of the shelves converter, you need to find one that is available locally.
Alternatively, if this AP8853 is monitored by DCE, you can use AP95MODBUS to get DCE to output AP8853's sensor via modbus TCP (up to 247 modbus slave ID per 1 DCE)
Regards,
Chris
(CID:128761886)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:36 PM . Last Modified: 2023-10-20 04:55 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.