Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 09:49 PM . Last Modified: 2024-04-09 01:39 AM
Hi,
we have the above APC PDUs installed in our 2 data centers.
I am wondering if the FTP settings on these PDUs need to be enabled for StruxureWare DCE to be able to apply updates to these devices.
thanks
Martin
(CID:105459374)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 09:49 PM . Last Modified: 2024-04-09 01:39 AM
Dear Martin,
Yes, FTP port needs to be enabled for the device. Please make sure that the following ports are open.
Protocol |
Transfer Protocol |
Ports |
Network |
Comments |
HTTP |
TCP (SSL) |
80 (443) |
Network speed of minimum 100 Mbps is recommended. Bandwidth usage between client and server heavily depends on number of discovered devices, alarm configuration and operations carried out in the client e.g. report generation. |
Communication from NetBotz Appliances / DCE Console/Web API and 3rd party integrations. |
SNMP |
UDP |
161 |
The bandwidth needed heavily depends on number of discovered devices, polling interval configured and alarm activity in the system. |
SNMP Communication between discovered devices and DCE |
SNMP (Trap) |
TCP/UDP |
162 |
Specified in device SNMP configuration |
SNMP Communication between discovered devices and DCE |
SMTP |
TCP |
25 |
Network requirements are low. Email traffic from the DCE is depended on alarm policy configuration and number of alarms occurring. |
Communication with e-mail server |
FTP |
TCP |
21 |
Used when device is discovered and DDF file transferred. The network requirements are low. |
Transfer DDF files between devices and DCE |
SCP |
TCP |
22 |
Used when device is discovered and DDF file transferred. The network requirements are low. |
Transfer DDF files between devices and DCE |
DNS |
TCP/UDP |
53 |
Very limited traffic and bandwidth requirement |
DNS server communication |
For more info: http://dcimsupport.apc.com/display/UADCE725/StruxureWare+Data+Center+Expert+Security |
You can also refer the below K-base: http://www2.schneider-electric.com/sites/corporate/en/support/faq/faq_main.page?page=content&country...
(CID:105459376)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 09:49 PM . Last Modified: 2024-04-09 01:39 AM
Dear Martin,
Yes, FTP port needs to be enabled for the device. Please make sure that the following ports are open.
Protocol |
Transfer Protocol |
Ports |
Network |
Comments |
HTTP |
TCP (SSL) |
80 (443) |
Network speed of minimum 100 Mbps is recommended. Bandwidth usage between client and server heavily depends on number of discovered devices, alarm configuration and operations carried out in the client e.g. report generation. |
Communication from NetBotz Appliances / DCE Console/Web API and 3rd party integrations. |
SNMP |
UDP |
161 |
The bandwidth needed heavily depends on number of discovered devices, polling interval configured and alarm activity in the system. |
SNMP Communication between discovered devices and DCE |
SNMP (Trap) |
TCP/UDP |
162 |
Specified in device SNMP configuration |
SNMP Communication between discovered devices and DCE |
SMTP |
TCP |
25 |
Network requirements are low. Email traffic from the DCE is depended on alarm policy configuration and number of alarms occurring. |
Communication with e-mail server |
FTP |
TCP |
21 |
Used when device is discovered and DDF file transferred. The network requirements are low. |
Transfer DDF files between devices and DCE |
SCP |
TCP |
22 |
Used when device is discovered and DDF file transferred. The network requirements are low. |
Transfer DDF files between devices and DCE |
DNS |
TCP/UDP |
53 |
Very limited traffic and bandwidth requirement |
DNS server communication |
For more info: http://dcimsupport.apc.com/display/UADCE725/StruxureWare+Data+Center+Expert+Security |
You can also refer the below K-base: http://www2.schneider-electric.com/sites/corporate/en/support/faq/faq_main.page?page=content&country...
(CID:105459376)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 09:49 PM . Last Modified: 2024-04-09 01:39 AM
Just to add to Bala's comments on FTP specifically, FTP (or scp if enabled) is also needed for firmware updates of the device from DCE.
(CID:105459399)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 09:49 PM . Last Modified: 2023-10-31 10:15 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.