A-Link Bus Power- Value alert- Overloaded

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

DCIM_Support
Picard
Picard
0 Likes
4
433

A-Link Bus Power- Value alert- Overloaded

This question was originally posted on DCIM Support by Ramu Manoharan on 2019-12-16


Hi All

 

I m keep getting the error A-Link Bus power - value alert - overloaded, this error coming every 3 mints and goes normal and again coming, can you any one help me on this what exactly causing this and how to fix. I'm having netbotz rack monitor 570 (netbotz91190F) DCE device.

Thanks in advance.

Thanks

Ramu

(CID:152570065)

4 Replies 4
DCIM_Support
Picard
Picard
0 Likes
1
433

Re: A-Link Bus Power- Value alert- Overloaded

This answer was originally posted on DCIM Support by Valentin Kozlov on 2019-12-16


Hi Ramu!

 

This error indicates that A-Link bus is overloaded. May be you have many sensor pods connected to Netbotz. If so, you need to add external power supply in the middle of the chain.

If there are no external devices connected to A-Link port, it indicates that your Netbotz is broken.

(CID:152570086)

DCIM_Support
Picard
Picard
0 Likes
0
433

Re: A-Link Bus Power- Value alert- Overloaded

This comment was originally posted on DCIM Support by Ramu Manoharan on 2019-12-16


Hi Valentin

Thanks for your reply...

this is an existing running environment, this error/issue started just 2 days before and there is no sensors added to the netbotz (recently or before the issue raises), kindly help.

 

Thanks

Ramu

(CID:152570095)

DCIM_Support
Picard
Picard
0 Likes
0
433

Re: A-Link Bus Power- Value alert- Overloaded

This answer was originally posted on DCIM Support by GavOB on 2019-12-17


Is there any sensor pods attached to the Netbotz at all? If so can you kindly remove?

 

If not and your device is under warranty can you contact local support as there maybe be a hardware problem.