2 DCE SERVER Mirror configuration

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • 2 DCE SERVER Mirror configuration
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:34 AM . Last Modified: ‎2024-04-05 04:32 AM

0 Likes
7
1392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:34 AM . Last Modified: ‎2024-04-05 04:32 AM

2 DCE SERVER Mirror configuration

I have 2 DCE 7.2.0 i want know How can i configuration mirror 2 dce server ?

can i do that like two server ?

 

(CID:126164008)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:34 AM . Last Modified: ‎2024-04-05 04:32 AM

0 Likes
5
1392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:34 AM . Last Modified: ‎2024-04-05 04:32 AM

Hi Hojjat,

there can be no real "mirrror" configuration in DCE. You can have 2 systems monitor the same devices but if you make a change in one, it will not be reflected on another. It will simply be 2 separate systems. Please keep in mind that NetBots should not be monitored by more than 2 DCE servers. 

 

Steve. 

(CID:126164051)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:34 AM . Last Modified: ‎2024-04-05 04:32 AM

In response to DCIM_Support
0 Likes
0
1392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:34 AM . Last Modified: ‎2024-04-05 04:32 AM

Hi Steven Marchetti,

Please keep in mind that NetBots should not be monitored by more than 2 DCE servers.

Ok, then two questions about NetBotz and 2+ DCE-servers:

  1. To which NetBotz devices this restriction applies (old NetBotz appliance, NetBotz-200 or new NetBotz-250)?
  2. What happens if this restriction is not met? What is the catch?

Very thanks for the support.

(CID:126164174)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:34 AM . Last Modified: ‎2024-04-05 04:32 AM

In response to DCIM_Support
0 Likes
0
1392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:34 AM . Last Modified: ‎2024-04-05 04:32 AM

spezialist, Original NetBotz that communicate via HTTP or HTTPS to DCE have issues with surveillance when being monitored by more than 2 DCE servers. Keep in mind that unlike SNMP that polls the current data only, DCE polls a NetBotz device (non SNMP) for ALL data that has been logged since last contact. This can put a great deal of strain on the system if you're trying to monitor by 3 or 4 systems AND trying to use surveillance especially. As an example of what can happen:
http://www.apc.com/us/en/faqs/index?page=content&id=FA158397 


Steve

(CID:126164349)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:35 AM . Last Modified: ‎2024-04-05 04:32 AM

In response to DCIM_Support
0 Likes
0
1392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:35 AM . Last Modified: ‎2024-04-05 04:32 AM

Hi Steven Marchetti,

Thanks for the clarification: i.e., the above limitation applies only to old NetBotz appliances and the new NetBotz-250 and only if video surveillance is used. Since I have a practical case, when NetBotz-450 is monitored by three DCE-servers (every minute) for several years. And so far I have not seen any problems at all, since there is no video surveillance.

Very thanks for the support.

(CID:126164547)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:35 AM . Last Modified: ‎2024-04-05 04:32 AM

In response to DCIM_Support
0 Likes
0
1392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:35 AM . Last Modified: ‎2024-04-05 04:32 AM

@spezialist, There is no official limitation, Like most things in NetBotz, there has been no limitation coded in so you can keep doing it until you can't. This is just something we've seen and troubleshot so it's what we recommend. You can add the devices to as many servers as you want but if you end up running into issues, the first thing you'll probably want to do is lower the load. Once you start alerting a lot and sending clips and doping surveillance, things can get out of hand very easy.

There has been no official testing with a full complement of sensors and cameras and numerous DCE servers monitoring it then doing surveillance and setting all thresholds to alert in every different possible alert action. That's pretty much what they'd have to do to officially set limits and still if you have 50 temp sensors, it may react differently than if you had 50 state sensors...just too many potential combinations to test.

 

The 250 is an SNMP device and has no surveillance option so it does not fall into this category. The surveillance issue I noted could be version 2 NetBotz (320, 420, 500) or version 3 (355, 45x, 550/570) devices.

 

Steve

(CID:126164577)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:35 AM . Last Modified: ‎2024-04-05 04:32 AM

In response to DCIM_Support
0 Likes
0
1392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:35 AM . Last Modified: ‎2024-04-05 04:32 AM

Hi Steven Marchetti,

Ok, thanks for the detailed explanation. I think it will be useful in my work.

Very thanks for the support.

(CID:126164665)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:35 AM . Last Modified: ‎2023-10-19 12:27 AM

0 Likes
0
1392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:35 AM . Last Modified: ‎2023-10-19 12:27 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore