Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

work order network connections lost

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • work order network connections lost
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:22 PM . Last Modified: ‎2024-04-03 12:50 AM

0 Likes
10
2667
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:22 PM . Last Modified: ‎2024-04-03 12:50 AM

work order network connections lost

Hi ,

In DCO 8.0.2 i need to move 2 network nexus 7000  from Rack1 in  DC1 to rack 12 in DC2

i wanted to do it in work order bat after i created the work order all the network connections on the source unit of nexus 7000 was deleted i did cancel the work order and still the nexus 7000 of the source  did not get the network connections back ,so because the DCO is in live DC so we did restore of the DB to point before the work order was created .

so now we gate the network connections back .

the questions is :

  1. way id it happened?
  2. is it a none issue in DCO 8.0.2?
  3. what is the way we can make work order for the units and do not lost the network connections!

Regards,

Yaniv Rozenbaum 

 

(CID:147202825)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 10
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:22 PM . Last Modified: ‎2024-04-03 12:50 AM

0 Likes
8
2667
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:22 PM . Last Modified: ‎2024-04-03 12:50 AM

Hi Yaniv,

Network/power cabling cannot be handled in Work order - and in general (for all DCo versions) by moving a server/device from one rack to another rack the possible network cabling may be cleared, so re-configuring may needed. 

Kind regards

(CID:147202971)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:22 PM . Last Modified: ‎2024-04-03 12:50 AM

In response to DCIM_Support
0 Likes
0
2667
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:22 PM . Last Modified: ‎2024-04-03 12:50 AM

Hi jef

my problem is not in the  in the target point i need to make the network connection 

the problem is server or network switch that as network connection if i make move by work order all the  network connection is lost from the original unit .

if this is in all the DCO Ver. - How can i make changes in my data center using Work Orders ?

if in any moving of server/switch i can not do it in Work Order whit out lost of data of network connection - what can i do whit the DCO?

Regards,

Yaniv Rozenbaum 

(CID:147203006)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:22 PM . Last Modified: ‎2024-04-03 12:50 AM

In response to DCIM_Support
0 Likes
0
2667
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:22 PM . Last Modified: ‎2024-04-03 12:50 AM

Hi Yaniv,

Unfortunately as I've mentioned, with or without work order if we move a server that has some network connections to another rack, then its network connections would be cleared (lost). So before making that move I would take a note of the existing network configuration so I can re-create after the move.  This the way software has been designed and works (for all versions). Actually in real data center usually we remove the cables (both power and network cables) before moving the server to another rack. 

Kind regards

(CID:147203354)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:22 PM . Last Modified: ‎2024-04-03 12:50 AM

In response to DCIM_Support
1 Like
0
2667
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:22 PM . Last Modified: ‎2024-04-03 12:50 AM

Hi Jef,
I really don't understand
one of the system's uses is to plan the future changes - in the computer room, which is used to preserve space in the cabinet for equipment that will come later from ather location.
That way every computer room seems to work in real life i think.
But what happens in the DCO is that when i did a future movemant to an equipment with a work order 
The equipment cuts off all network connectivity on the exists unit as if the transition had already been made in practice, which did not happen in reality because it is a future activity (pland to the end of the year) .
Is there another way to use move unit in work order?

I found workaround I am copying existing equipment and renamingin it to mark it as something in the future in the target cabinet. 
is the only option - i do it without a work order !

My client asks if we didn't use work orders for the planning of the changes we do in the data center so what the work order use for ?
from his point - If it is for only introduction for new equipment only ... it seems a little unnecessary ...

 

Kind regards,

yaniv

(CID:147784993)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:22 PM . Last Modified: ‎2024-04-03 12:50 AM

In response to DCIM_Support
0 Likes
0
2667
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:22 PM . Last Modified: ‎2024-04-03 12:50 AM

Yaniv

You are referring to movement of a device using work orders and network connections? In the below example my original server is in the left rack at U28 (circled below). That server has several network connections to a patch panel at the top of this rack. 

I ran a test in my own demo environment. I moved the server circled below to the rack on the right side rack U23 (also circled below) and made a network connection from this new location to the patch panel at the top of the new rack.

I noticed when I created this planned task, the network connections on my original server (on the left) now appear to be removed when I use the network tool. Only the planned connections seem to exist when I use the network tool.

Is this what you're reporting?

Regards

Greg Sterling

(CID:147785223)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:23 PM . Last Modified: ‎2024-04-03 12:50 AM

In response to DCIM_Support
0 Likes
0
2667
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:23 PM . Last Modified: ‎2024-04-03 12:50 AM

Actually the original network connections are really purged/deleted as if I cancel the workorder the original network connections remain lost.

(CID:147785229)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:23 PM . Last Modified: ‎2024-04-03 12:50 AM

In response to DCIM_Support
0 Likes
0
2667
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:23 PM . Last Modified: ‎2024-04-03 12:50 AM

Hi Greg ,

yes, that is my problam the original network connections are really purged/deleted!

Sorry it took me a while To answer but I was on vacation.

so as i understand from your test the problem exists not only in my version 8.0.2 but also in the most updated version of the system.

The customer asks if now that we have found out the problem can it be fixed
in the next version of the system or otherwise?

 

Kind regards,

Yaniv Rozenbaum .

(CID:148766811)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:23 PM . Last Modified: ‎2024-04-03 12:50 AM

In response to DCIM_Support
0 Likes
0
2667
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:23 PM . Last Modified: ‎2024-04-03 12:50 AM

Hi

The customer asks if now that we have found out the problem can it be fixed
in the next version of the system or otherwise?

 

Kind regards,

Yaniv Rozenbaum .

(CID:149783361)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:23 PM . Last Modified: ‎2024-04-03 12:50 AM

In response to DCIM_Support
0 Likes
0
2667
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:23 PM . Last Modified: ‎2024-04-03 12:50 AM

Hi Yaniv,

I'm sorry to disappoint you, it is working as designed. As mentioned already if we move a server that has network configurations to another location/rack, then its network connections would be cleared. So before making the move it is recommended to take note of the connections, so they can be recreated again (by user).

Kind regards 

(CID:149783369)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 09:23 PM . Last Modified: ‎2023-10-22 09:39 PM

0 Likes
0
2667
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:23 PM . Last Modified: ‎2023-10-22 09:39 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore