I'm monitoring a Circutor modbus devices. There are 27 slaves with the same modbus IP address and periodically some slaves are lossing connection.
(CID:116361027)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 02:33 PM . Last Modified: β2024-04-08 01:16 AM
Hi Enric Climent,
Yesterday officially released the new DCE-7.4.3: StruxureWare Data Center Expert v7.4.3 Release Notes. And as it is written in the release:
Improvements to Modbus polling
Modbus polling is no longer affected by prolonged network disruptions.
Therefore, this may be another recommendation in the form of item number 5. Try it.
With best regards.
P.S.: In addition, here more detailed information from Jackie Lehr on this news subject on my question:
Q: Explain, please, in more detail, what do you mean? How is this achieved?
A: There was an issue where Modbus polling consumed resources if network connectivity was interrupted for an extended period. It is now fixed.
(CID:116920091)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 02:33 PM . Last Modified: β2024-04-08 01:16 AM
Hi Enric Climent,
Unfortunately, at such number of Modbus slave devices it is normal π. I often meet similar problems. There are my recommendations:
As option it is possible to reduce number of sensors, which are read out on Modbus slave devices.
And at last, to try to understand, and probably to reveal and eliminate defects of the Modbus serial communication line between Modbus devices. Practically, the last recommendation can be the most effective and useful.
With best regards.
(CID:116361050)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 02:33 PM . Last Modified: β2024-04-08 01:16 AM
Hi Enric Climent,
Yesterday officially released the new DCE-7.4.3: StruxureWare Data Center Expert v7.4.3 Release Notes. And as it is written in the release:
Improvements to Modbus polling
Modbus polling is no longer affected by prolonged network disruptions.
Therefore, this may be another recommendation in the form of item number 5. Try it.
With best regards.
P.S.: In addition, here more detailed information from Jackie Lehr on this news subject on my question:
Q: Explain, please, in more detail, what do you mean? How is this achieved?
A: There was an issue where Modbus polling consumed resources if network connectivity was interrupted for an extended period. It is now fixed.
(CID:116920091)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 02:33 PM . Last Modified: β2023-10-22 09:36 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.