service is starting grab a cup of coffee

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • service is starting grab a cup of coffee
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
127
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:37 PM . Last Modified: ‎2024-04-07 11:42 PM

0 Likes
10
1491
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:37 PM . Last Modified: ‎2024-04-07 11:42 PM

service is starting grab a cup of coffee

I am receiving the a splash screen stating "Service is starting.  Grab a cup of coffee and we'll be ready in a minute" when trying to access the DCO.  I have tried HTTPS:// with the IP and the FQDN.   Has anyone found a solution besides the one that I found that stated to use the server name instead of the IP? 

 

 

(CID:123346836)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 10
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:37 PM . Last Modified: ‎2024-04-07 11:42 PM

0 Likes
0
1491
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:37 PM . Last Modified: ‎2024-04-07 11:42 PM

Hello Krista.

Are you able to logon to your DCO server's webmin interface at https://:10000/ and check the status page to confirm whether DCO services are running?

Which version of DCO are you running?

Regards

Greg Sterling

(CID:123346849)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:38 PM . Last Modified: ‎2024-04-07 11:42 PM

0 Likes
0
1491
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:38 PM . Last Modified: ‎2024-04-07 11:42 PM

Thanks for your quick response.  I am new to the application, so please bear with me.  I am able to login to webmin.  We are running DCO ver. 8.0.4.  I have attempted to check the status by clicking on "Status" under "StruxureWare DC Operation" but every time I click on that it brings up the Setup page.

(CID:123346875)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:38 PM . Last Modified: ‎2024-04-07 11:42 PM

0 Likes
0
1491
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:38 PM . Last Modified: ‎2024-04-07 11:42 PM

You mention you clicked the "status" item (highlighted below) and you see the setup page?

 

 

If you select the "system information" item also highlighted above, are the memory and local disk space entries (circled above) showing values which meet the system requirements for your DCO server?

Is your server newly installed or had it been running for a while and it has recently stopped?

We may need you to click the "download log files" (a few entries above the status link) so we can check the log entries to see what has gone wrong.

Regards

Greg Sterling

(CID:123346878)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:38 PM . Last Modified: ‎2024-04-07 11:42 PM

0 Likes
0
1491
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:38 PM . Last Modified: ‎2024-04-07 11:42 PM

After poking around, I don't believe that this application has been completely setup.  I'm checking with the folks that did the install on our end.  That could definitely be my problem.

 

(CID:123346881)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:38 PM . Last Modified: ‎2024-04-07 11:42 PM

0 Likes
0
1491
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:38 PM . Last Modified: ‎2024-04-07 11:42 PM

It is a brand new install.  I am able to view the system info.  When I click on download log files it brings me right to the setup.  I don't think that it was completely configured.

 

(CID:123346883)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:38 PM . Last Modified: ‎2024-04-07 11:42 PM

0 Likes
0
1491
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:38 PM . Last Modified: ‎2024-04-07 11:42 PM

I agree. Is this a centos installation or redhat?

Greg

(CID:123346885)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:38 PM . Last Modified: ‎2024-04-07 11:42 PM

0 Likes
0
1491
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:38 PM . Last Modified: ‎2024-04-07 11:42 PM

centos

(CID:123346887)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:38 PM . Last Modified: ‎2024-04-07 11:42 PM

0 Likes
0
1491
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:38 PM . Last Modified: ‎2024-04-07 11:42 PM

Based on what you're describing it does seem like something is not setup correctly.

Greg

(CID:123346901)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:38 PM . Last Modified: ‎2024-04-07 11:42 PM

0 Likes
0
1491
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:38 PM . Last Modified: ‎2024-04-07 11:42 PM

Hi Krista,
I'm also agree with Greg, that based on the description it appears something is not setup correctly. Particularly, when you are prompted/forwarded to the setup page it appears that during the initial installation you might have chosen a cluster installation (and now the full cluster setup seems to be not completed yet). So if the intention is to have an stand-alone server, then you would need to re-install the software, but during the installation select "Install Standalone":

For system recommendations please see the following page: System requirements

I would also recommend installing the latest version (currently DCO 8.1).

Kind regards

(CID:123347500)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:38 PM . Last Modified: ‎2023-10-22 09:36 PM

0 Likes
0
1491
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:38 PM . Last Modified: ‎2023-10-22 09:36 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore