A customer has a camera Pelco IJP121-1IS and a Netbotz 570 and I want to know if I need to manage the camera trough the Netbotz or direct with DCE via SNMP.
Best regards,
Enric Climent
(CID:126183478)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:38 AM . Last Modified: 2024-04-05 03:46 AM
you have to configure and detect the camera in NB570, and in DCE you need licences and configure the camera as a NB device.
But i detect some issue in the comunication between NB and DCE than can´t resolve.
(CID:126183488)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:38 AM . Last Modified: 2024-04-05 03:46 AM
Hi Enric,
The only way to view images of a supported Pelco camera in DCE is to monitor that camera via NetBotz appliance and then have DCE monitor that appliance. You may be able to add the device to DCE using SNMP but the only thing you'll get there are SNMP values and no images. I'm not sure what values you'd get via SNMP and I don't believe there are any current DDFs.
Steve
(CID:126183490)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:38 AM . Last Modified: 2023-10-22 04:41 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.