importing network connections from ETL

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • importing network connections from ETL
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:02 PM . Last Modified: ‎2024-04-09 03:59 AM

0 Likes
5
1290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:02 PM . Last Modified: ‎2024-04-09 03:59 AM

importing network connections from ETL

I've created a job to import network connections through the ETL. The job runs four transformations to import data to the follow tables in this order: configuration_item, configuration_item_realtion, relation_endpoint_property and relatio_property. The job runs well and insert the records, the state_flad field in configuration_item table is synced but in the other tables is new. And any connection is imported in SWO. I've tried to associate the servers and then run again the job, but any connection is imported too.

Which is the best practice to do this connection import?

Best regards,

 

Enric

(CID:100340565)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:02 PM . Last Modified: ‎2024-04-09 03:59 AM

0 Likes
3
1290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:02 PM . Last Modified: ‎2024-04-09 03:59 AM

Hi Enric

In previous versions of DCO you had to use the configuration_item_relation and relation_endpoint_property to import network connections. This approach however had some difficulties, especially with deleting connections and ports.

The current way of importing port configurations and network connections is to put the data in the tables port_configuration and network_connection. The work you have already done for the configuration items can be reused, as this is also needed in the new approach.

Information on the tables can be found here: ETL Import Database

I will check if the documentation clearly enough specifies that you can no longer use the tables configuration_item_relation and relation_endpoint_property to import network connections.

Hope this helps.

Best,

Niels

------------------------------------------------------

EDIT: I have attached files showing how you can do this.

Network Import.kjb

ConfigurationItems.ktr

Network.ktr

PortConfiguration.ktr




(CID:100340602)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:02 PM . Last Modified: ‎2024-04-09 03:59 AM

0 Likes
3
1291
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:02 PM . Last Modified: ‎2024-04-09 03:59 AM

Hi Enric

In previous versions of DCO you had to use the configuration_item_relation and relation_endpoint_property to import network connections. This approach however had some difficulties, especially with deleting connections and ports.

The current way of importing port configurations and network connections is to put the data in the tables port_configuration and network_connection. The work you have already done for the configuration items can be reused, as this is also needed in the new approach.

Information on the tables can be found here: ETL Import Database

I will check if the documentation clearly enough specifies that you can no longer use the tables configuration_item_relation and relation_endpoint_property to import network connections.

Hope this helps.

Best,

Niels

------------------------------------------------------

EDIT: I have attached files showing how you can do this.

Network Import.kjb

ConfigurationItems.ktr

Network.ktr

PortConfiguration.ktr




(CID:100340602)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:02 PM . Last Modified: ‎2024-04-09 03:59 AM

In response to DCIM_Support
0 Likes
0
1290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:02 PM . Last Modified: ‎2024-04-09 03:59 AM

Hi Niels,

 

Thanks for your input but I've tried to work with port_configuration and network_connection tables and it doesn't work too.

Do you have any document or sample to do this network integration with ETL?

Best regards,

 

Enric

 

(CID:100340670)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:02 PM . Last Modified: ‎2024-04-09 03:59 AM

In response to DCIM_Support
0 Likes
0
1290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:02 PM . Last Modified: ‎2024-04-09 03:59 AM

I have updated my answer to include some transformations files that should help.

(CID:100340678)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:03 PM . Last Modified: ‎2024-04-09 03:59 AM

In response to DCIM_Support
0 Likes
0
1290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:03 PM . Last Modified: ‎2024-04-09 03:59 AM

Hi Niels,

 

Thanks for your help. With your sample files I've got to import the network connections.

Best regards,

 

Enric

 

(CID:100340891)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 03:03 PM . Last Modified: ‎2023-10-31 11:08 PM

0 Likes
0
1290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 03:03 PM . Last Modified: ‎2023-10-31 11:08 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore