Posted: 2022-05-26 08:20 AM
Hello,
I have run into some i2 controllers that seem to be stuck in bootloader mode (the version # reads 0). They fail when trying to "download all objects" giving me a BACnet module plugin error (they aren't BACnet controllers so I am lost on that). I would like to flash the firmware to see if I can get them back to normal operating capacity without having to replace the controllers all together, but I can't seem to find out how to flash firmware in Ecostruxure 2.0.4.83. These were all Andover Continuum sites with net controllers before a migration to Schneider AS-P controllers to replace the failing net controllers.
Thank you,
BW
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-05-26 04:58 PM
i2 firmware upgrade is not supported in EBO and it's not really a priority since no new i2 firmware has been released in over 10 years.
You can use the ROAM IO service tool to update i2 controllers one at a time. You may need to perform a hard reset on the i2 controller and then upgrade the firmware with ROAM IO.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-05-26 04:58 PM
i2 firmware upgrade is not supported in EBO and it's not really a priority since no new i2 firmware has been released in over 10 years.
You can use the ROAM IO service tool to update i2 controllers one at a time. You may need to perform a hard reset on the i2 controller and then upgrade the firmware with ROAM IO.