connected APC PDUs UPS and inrows to DCE and got ddf error. We scan connect to the devices and the sensor of the devices are available, but they remain on error
(CID:140215986)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 05:03 PM . Last Modified: β2024-04-03 04:17 AM
Hi, what is the PN for PDU, UPS & Inrow?
Did you search for right ddfs on ddf site?
What is the error message?
(CID:140216011)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 05:03 PM . Last Modified: β2024-04-03 04:16 AM
UPS APC Smart-UPS SRT 8000VA RM 230
Inrow ACRD101
PDUs AP8958As
There were default ddf files for APC devices on DCE so we have not look for them. Is it required?
(CID:140216009)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 05:03 PM . Last Modified: β2024-04-03 04:16 AM
Hi Oscar,
If you're getting a DDF transfer error "Device status may be inaccurate due to attempt to transfer DDF failed", please check out k-base FA177004. It describes the reason for the error and how to resolve it.
Thanks,
Steve
(CID:140216013)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 05:03 PM . Last Modified: β2024-04-03 04:16 AM
Steven Marchetti sent link to check if you have FTP protocols blocked on SNMP cards.
I think this he is right regarding the issue.
Also it is good to update ddf files, no matter if it is APC equipment.
Personally I couln`t get data from AP8858 without updating PDU ddf file.
(CID:140216020)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 05:03 PM . Last Modified: β2024-04-03 04:16 AM
Dear oscar dafauce,
Tell us, please, did you solve your problem or not?
With respect.
(CID:141269285)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 05:03 PM . Last Modified: β2024-04-03 04:16 AM
We got snmp walkfile and waiting for ddf to be developed for these systems
(CID:141269294)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 05:04 PM . Last Modified: β2024-04-03 04:16 AM
Ok, thanks for the good feedback π.
(CID:141269333)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 05:04 PM . Last Modified: β2023-10-22 04:27 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Youβve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.