camera pod 165 Live view issue in netbotz 755
EcoStruxure IT Forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Let's start with a few smaller ticket items before delving into more advanced troubleshooting.
Was the camera feed showing at some point in the past or has been showing the error message since installation?
Is the appliance running firmware 5.4.0? You can check the firmware by clicking on superuser in the upper-right and then about.
This firmware was just recently released and I would recommend upgrading to it before proceeding with troubleshooting. If the appliance is not on 5.4.0 or 5.3.5, you will need to upgrade to 5.3.5 before proceeding with the 5.4.0 upgrade. The firmware can be found on the product page on apc.com in the downloads section: https://www.apc.com/us/en/product/NBWL0755/wall-mount-security-and-environmental-appliance-netbotz-7...
Instructions on installing the firmware can be found in the NetBotz Room Monitor 755 Installation and Quick Start guide found on the product page as well under Documents.
It does not appear from the screen capture that you are using any additional sensor or rack access pods, but if you are, ensure that an A-Link terminator is installed correctly: https://www.se.com/us/en/faqs/FAQ000224706/
A common issue that leads to this specific scenario is that there isn't enough POE power (POE+) being provided by the switch. Information this can be found here: https://www.apc.com/us/en/faqs/FAQ000221237/
I also recommend resetting the integrated camera by unscrewing the set screw at the back of the appliance and then reseating the camera. Careful not to over tighten the set screw when reconnecting.
Let us know the results and details of the above and we can look into this further if needed.