Will DCO 8.1 install in the following hardware - DL360 Gen 10

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Will DCO 8.1 install in the following hardware - DL360 Gen 10
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
128
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:01 AM . Last Modified: ‎2024-04-05 04:43 AM

0 Likes
5
1032
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:01 AM . Last Modified: ‎2024-04-05 04:43 AM

Will DCO 8.1 install in the following hardware - DL360 Gen 10

Will DCO 8.1 install in the following hardware:

HPE ProLiant DL360 Gen10 4114 85W 1P 16G-2R P408i-a 8SFF Base Server

  • ·         4114 (10-Core, 2.2 GHz, 85W)
  • ·         32 GB RDIMM 2R 2666 MT/s  (2x 16 GB)
  • ·         2 x HPE 600GB SAS 12G Enterprise 10K SFF (2.5in) SC 3yr Wty Digitally Signed Firmware HDD ( or HPE 400GB SAS 12G Mixed Use SFF (2.5in) SC 3yr Wty Digitally Signed Firmware SSD) configured as RAID 1

(CID:125213394)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:01 AM . Last Modified: ‎2024-04-05 04:43 AM

0 Likes
2
1033
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:01 AM . Last Modified: ‎2024-04-05 04:43 AM

Hi John MacDonald,

According to the information on page System requirements, we have:

Recommended StruxureWare Data Center Operation server configuration Server requirement guidelines (minimum)
  • CPU: 4 cores minimum. We recommend 8 cores
  • Memory: 16 GB RAM (absolute minimum requirement)
  • 100 GB storage, speed minimum 170 MB/s
  • Cluster network: 1 Gbps connection between nodes
  • Disaster recovery network: 10 Mbps with low latency <100 ms 

If your'e installing DCO on an existing server, note that DCO claims almost all memory (JVM about 8 GB and Postgres about 6 GB alone). Therefore, you may experience issues if you have other applications running on the server, such as surveillance and monitoring agents.

Server requirement guidelines for 10,000 racks across 200 rooms with 30 concurrent users
  • 8 CPU cores
  • 32 GB RAM
  • 1 Gbps network connection between cluster nodes
  • 100 GB storage, speed minimum 170 MB/s
Server requirement guidelines for 20,000 racks across 400 rooms with 30 concurrent users
  • 16 CPU cores
  • 64 GB RAM
  • 1 Gbps network connection between cluster nodes
  • 100 GB storage, speed minimum 170 MB/s

Thus, your physical server is no problem with DCO configuration up to 10,000 racks (which probably exceeds your real needs).

With respect.

(CID:125213407)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:01 AM . Last Modified: ‎2024-04-05 04:43 AM

0 Likes
2
1034
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:01 AM . Last Modified: ‎2024-04-05 04:43 AM

Hi John MacDonald,

According to the information on page System requirements, we have:

Recommended StruxureWare Data Center Operation server configuration Server requirement guidelines (minimum)
  • CPU: 4 cores minimum. We recommend 8 cores
  • Memory: 16 GB RAM (absolute minimum requirement)
  • 100 GB storage, speed minimum 170 MB/s
  • Cluster network: 1 Gbps connection between nodes
  • Disaster recovery network: 10 Mbps with low latency <100 ms 

If your'e installing DCO on an existing server, note that DCO claims almost all memory (JVM about 8 GB and Postgres about 6 GB alone). Therefore, you may experience issues if you have other applications running on the server, such as surveillance and monitoring agents.

Server requirement guidelines for 10,000 racks across 200 rooms with 30 concurrent users
  • 8 CPU cores
  • 32 GB RAM
  • 1 Gbps network connection between cluster nodes
  • 100 GB storage, speed minimum 170 MB/s
Server requirement guidelines for 20,000 racks across 400 rooms with 30 concurrent users
  • 16 CPU cores
  • 64 GB RAM
  • 1 Gbps network connection between cluster nodes
  • 100 GB storage, speed minimum 170 MB/s

Thus, your physical server is no problem with DCO configuration up to 10,000 racks (which probably exceeds your real needs).

With respect.

(CID:125213407)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:01 AM . Last Modified: ‎2024-04-05 04:43 AM

In response to DCIM_Support
0 Likes
0
1032
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:01 AM . Last Modified: ‎2024-04-05 04:43 AM

Thanks for your comments but I was asking due to the RAID controller - please confirm DCO 8.1 will install on this device, thanks!

(CID:125213425)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:01 AM . Last Modified: ‎2024-04-05 04:43 AM

In response to DCIM_Support
0 Likes
0
1033
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:01 AM . Last Modified: ‎2024-04-05 04:43 AM

Hi John MacDonald,

In your question, you did not ask about the RAID controller 😀.

And yet, according to the official specification for the HPE Smart Array P408i-a Controller on page HPE Smart Array P408i-a Controller - Overview, its guaranteed support for CentOS Linux (see also file HPE Smart Array Operating System Support Matrix). Let me remind you that DCO-8.1 is based on CentOS-7 Linux.

With respect.

(CID:126158687)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:02 AM . Last Modified: ‎2024-04-05 04:43 AM

0 Likes
0
1032
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:02 AM . Last Modified: ‎2024-04-05 04:43 AM

Hi John MacDonald,

Have you solved your problem or not?

With respect.

(CID:126159012)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 12:02 AM . Last Modified: ‎2023-10-22 04:22 AM

0 Likes
0
1032
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 12:02 AM . Last Modified: ‎2023-10-22 04:22 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore