Before upgrading to the latest DCE version, I would like to download the latest client software and allow our IT department to pre-package the software
I used to download the client from http://isxc.apc.com/desktop/ which is not available any more.
Where I can download the client now?
Thanks, Yang.
(CID:134681127)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 12:30 PM . Last Modified: 2024-04-04 12:50 AM
Hi Yang,
The DCE thick client is only downloadable from the server itself. There's no download executable from the Schneider web page. If you don't want to upgrade your current DCE server until you've tested the install, I suggest deploying a trial VM of 7.6. You'll have bot the client software as well as a server to which to attach. Without that, the client is useless anyway.
Thanks,
Steve
(CID:134681144)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 12:30 PM . Last Modified: 2023-10-22 04:20 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.