I am trying to find the sensor ID of a specific sensor in DCE so I can call it using SOAP but it doesn't seem to be in any of the columns. Is this a value I need to assign or am I looking in the wrong place?
To clarify I need the ID to use in the following field:
Thank you
(CID:140708326)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 05:28 PM . Last Modified: 2024-04-03 03:21 AM
Hi Neil,
First, you need to have the ID for the device. The following SOAP request should get you a list of devices discovered on your DCE server.
http://
Your response should be a sequence of
Once you have that, you can use this next SOAP request to get a list of sensors for a given device:
http://
Your response should be a series of
Hope this answers your question.
Regards,
Glenn Martin
(CID:140708356)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 05:28 PM . Last Modified: 2024-04-03 03:21 AM
Hi Neil,
First, you need to have the ID for the device. The following SOAP request should get you a list of devices discovered on your DCE server.
http://
Your response should be a sequence of
Once you have that, you can use this next SOAP request to get a list of sensors for a given device:
http://
Your response should be a series of
Hope this answers your question.
Regards,
Glenn Martin
(CID:140708356)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 05:28 PM . Last Modified: 2024-04-03 03:21 AM
Hi Glenn,
Thank you for the quick response. This was exactly what I was looking for.
Appreciate it
(CID:140708366)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 05:28 PM . Last Modified: 2023-10-22 04:19 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.