Posted: 2021-03-30 07:30 PM
If When I add DCE Nodes license 100 Nodes, The Server ( DCE ) will be reboot or Not ?
In my past experience, The System was re-boot, When I add the license key in the DCE
So I want to know at this time again , Before I add the license key
Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-31 01:06 AM
Hi Doody,
I tested this moment ago (on my DCE 7.8.1), by adding extra nodes license key I do get the notification 'Adding a new license key may cause StruxureWare Data Center Expert to reboot.':
But it did not reboot in my test. So extra node license added without server reboot.
By the way, 7.2.7 is many versions behind, so you/customer might want to consider upgrading.
Kind regards,
Jef
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-31 01:06 AM
Hi Doody,
I tested this moment ago (on my DCE 7.8.1), by adding extra nodes license key I do get the notification 'Adding a new license key may cause StruxureWare Data Center Expert to reboot.':
But it did not reboot in my test. So extra node license added without server reboot.
By the way, 7.2.7 is many versions behind, so you/customer might want to consider upgrading.
Kind regards,
Jef
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.