Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Heat Map Issues & Warnings

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Heat Map Issues & Warnings
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
barlasbaycik1
barlasbaycik1
Explorer

Posted: ‎2021-03-25 11:14 AM . Last Modified: ‎2025-04-02 11:38 PM

0 Likes
3
5744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-25 11:14 AM . Last Modified: ‎2025-04-02 11:38 PM

Heat Map Issues & Warnings

Hello I am living issues about 3d heat map. Could you please help me about this issue?

1)This 1st floor we don’t have any issue in this flat. I will locate sensor in cabinet. Probably that will solve my problem in this flat.


2)This is first basement floor. you may see picture at the attachment.
The error is one or more rack has server but no airflow. I erased necessary server I solved this problem. But 3d temperature map doesn’t fill color everywhere.

 

3)The error is insufficient cooling. So the temperature may be inaccurate. Also 3d temperature map doesn’t fill color everywhere. I need help for this issue.

 

4)The error is insufficient cooling. So the temperature may be inaccurate. Also 3d temperature map fill color everywhere. They doesn’t’ want color outsite of the cabinet rows. I need help for this issue.

 

The error is insufficient cooling. So the temperature may be inaccurate. Also 3d temperature map doesn’t fill color everywhere. I need help for this issue.

Attachments
Labels
  • Labels:
  • IT Design CFD
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
gsterling
gsterling Mentor
Mentor

Posted: ‎2021-03-25 01:17 PM

0 Likes
2
5735
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-25 01:17 PM

Hello Barlas

 

In the screenshots you provided you have the "measured plane" button selected. This means the calculation will be based on sensor information in the rooms. When in "measured plane" mode, the 3D view gives each sensor a range of influence which is a few feet from the sensor. This is why there are areas in the few with no color coding as how should a CFD calculated based on measurements in an area of the room there are no sensors within a long distance?

 

The "calculated pane" in the 3D view will estimate for the entire room based on estimated load and the physical devices in the room whether or not sensors are present.

 

In the containment systems in screenshot #4, do you have gaps (open areas)? It looks like it based on the screenshot. Containment systems need to be completely filled, so if there are areas where no racks or devices are inside, I would suggest placing an object like a think block in that spot to fill the space between the cabinets on either side of the openings. Containment systems must also be tight around the cabinets inside, so there cannot be spaces between the cabinets and on the ends.

 

We may need more info to diagnose cooling issues in some of the other rooms.

 

Regards

 

Greg Sterling

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

barlasbaycik1
barlasbaycik1
Explorer

Posted: ‎2021-03-28 10:46 PM

In response to gsterling
0 Likes
1
5724
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-28 10:46 PM

Hello Greg,

 

Thanks for reply. I tried lots of things. But I couldn't be successful. I believe that ı have diffrent issue. Because I locate wirless Temp and Hummdidty Sensors  to fill with color. But it didn't worked. I will try to re-build the rooms. ıf you can halp me I can also prvide you more information.

 

Best Regards,

Barlas.

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

gsterling
gsterling Mentor
Mentor

Posted: ‎2021-04-01 09:42 AM

In response to barlasbaycik1
0 Likes
0
5692
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-01 09:42 AM

Hello Barlas, just a quick update.

 

I have avoided responding here as you are also working with Jef via the support ticket system. Jef and I work on the same overall team and he's an excellent resource for inquires of this nature. 

 

Regards

 

Greg Sterling

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore