Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

WIB 8000 shows disconnected immediately after being added to Data Center Expert v.8.3.0

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • WIB 8000 shows disconnected immediately after being added to Data Center Expert v.8.3.0
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
Angwenyi
Angwenyi
Explorer

Posted: ‎2025-03-16 06:46 AM

0 Likes
5
1797
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-16 06:46 AM

WIB 8000 shows disconnected immediately after being added to Data Center Expert v.8.3.0

Dear Team,

I have downloaded the two DDF from the DDF search but whenever I add Stulz WIB 8000 it's added but after initializing it immediately shows disconnected. This is after using both the Modbus and SNMP DDF with Modbus and SNMP device add respectively.

I have configured the WIB 8000 to port 161 under SNMP settings, I also did an SNMP walk and attached is the walk file.

Kindly anyone who has had this problem and was able to sort it out, would appreciate to know how you did it.

Thank you.

Attachments
Stulz WIB8000 - SNMP Device Walk.txt
Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
Gabi
Gabi
Mentor

Posted: ‎2025-03-17 07:41 AM

1 Like
1
1773
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-17 07:41 AM

Hello,

 

first of all, WIB 8000 it is a kind of gateway....not the equipment itself

 

from your snmp walk I see a timeout at the end...so you have network problems or WIB it is not properly configured on the equipment's side (I see that you have 2 units attached?)

When adding a device on snmp, DCE trying a full walk in order to match oid with internal database...if the walk timeout occur, DCE cannot add the device  

 

Also, reboot WIB after you modify configuration

 

from specs seems like WIB 8000 does not have modbus tcp option...modbus DDF available can be used if you install a gateway from RS485 to modbus TCP(without wib8000)

Reply

Link copied. Please paste this link to share this article on your social media post.

ATrabert
ATrabert Mentor
Mentor

Posted: ‎2025-03-18 05:42 AM

1 Like
2
1754
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-18 05:42 AM

Hi,

I'm able to simulate it with some of our internal SE tools used for DDF testing, so the DDF works. Just to confirm, you're using SNMPv1 when you try to discover it?  If you're using snmpv3, please try snmpv1.

If it discovers then immediately goes into a failure state, the device is getting hung up on one of the OIDs used by DCE to discover other devices or an oid in the DDF itself.  

The best way to troubleshoot this would be to open a case with DCE tech support and the DDF team.  I'd also recommend removing any 3rd party DDFs that you know you are not using.  I've seen geist ddfs cause this with some devices, but again it could be any discovery OID used by other DDFs in DCE or an OID in the WIB8000 DDF itself.  Providing DCE capturelogs and having tech support run a packet capture from the DCE backend is the quickest way to figure this out.

ATrabert_0-1742301133475.png

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Angwenyi
Angwenyi
Explorer

Posted: ‎2025-03-18 07:06 AM

In response to ATrabert
0 Likes
1
1722
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-18 07:06 AM

Hi ATrabert,

Thank you for your response.

Am using SNMPv1, all DDF used are downloaded from https://ddf.ecostruxureit.com/

Is there an email for tech support I can use to follow up on the same.

Thank you.

Reply

Link copied. Please paste this link to share this article on your social media post.

Angwenyi
Angwenyi
Explorer

Posted: ‎2025-03-19 02:26 AM

In response to Gabi
0 Likes
0
1715
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-19 02:26 AM

Hi Gabi,

Kindly what do you advise I should check on considering am using SNMPv1 and not Modbus.

I have rebooted the WIB8000 severally but still no success.

Thank you.

Reply

Link copied. Please paste this link to share this article on your social media post.

Cory_McDonald
Cory_McDonald Champion
Champion

Posted: ‎2025-03-19 04:15 AM

In response to Angwenyi
0 Likes
0
1716
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-19 04:15 AM

Hello @Angwenyi,

 

You can use the following form to reach out to DCE technical support: https://app.ecostruxureit.com/request/

 

Regards,

Cory

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore