Dear Community,
We are testing VIZOR on iphone with DCO version 7.4.5. While testing with port 80 with the correct username and password, VIZOR has no problem displaying information from DCO itself. When we changing port 80 to 443, VIZOR shows error "A license for struxureware: capacity is needed to show capacity data" as shown below:

We later repeat the test with Andriod phone with the same version of DCO and port 443. The result is "Data not available – The server could not send the requested data. Try again." Port 80 is working with no issue.

Question:
(CID:100340935)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 03:11 PM . Last Modified: 2024-04-09 03:56 AM
Hi Law,
Vizor is not supporting port 443. Only port 80 can be used.
Some more information regarding Vizor including port configuration is found here: http://dcimsupport.apc.com/display/public/UAOp74/StruxureWare+Data+Center+Operation%3A+VIZOR
/Søren
(CID:101027885)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 03:11 PM . Last Modified: 2024-04-09 03:56 AM
Hi Law, thank you for posting. Let's see if we can find someone, who can be of assistance here. @community - any ideas?
(CID:101027855)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 03:11 PM . Last Modified: 2024-04-09 03:56 AM
Hi Law,
Vizor is not supporting port 443. Only port 80 can be used.
Some more information regarding Vizor including port configuration is found here: http://dcimsupport.apc.com/display/public/UAOp74/StruxureWare+Data+Center+Operation%3A+VIZOR
/Søren
(CID:101027885)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 03:11 PM . Last Modified: 2024-04-09 03:56 AM
Hi Søren, Thanks for the reply!
(CID:101027893)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 03:11 PM . Last Modified: 2023-10-31 11:41 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.