Using APC Switches and configuring LAN2 on Vitual DCE

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Using APC Switches and configuring LAN2 on Vitual DCE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
112
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:52 AM . Last Modified: ‎2024-04-08 03:11 AM

0 Likes
2
1139
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:52 AM . Last Modified: ‎2024-04-08 03:11 AM

Using APC Switches and configuring LAN2 on Vitual DCE

Hi,

We are planning a new setup where we have 5 nos. APC Switches (AP9224110) which will be cascaded and connected to an Ethernet Port on an IBM Server. This port will be configured for private connection (192.168.x.x) for a Virtual DCE Server 7.4.x to assign DHCP address for the peripheral devices.

Can anyone share the LAN2 Virtual DCE configuration document link and if any concerns in this setup.

 

Thanks & Regards

Shemil

(CID:110015138)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:53 AM . Last Modified: ‎2024-04-08 03:11 AM

0 Likes
0
1137
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:53 AM . Last Modified: ‎2024-04-08 03:11 AM

Dear Shemil,

I have provided the following DCE Server requirements to one of the Customers. I am sharing the same to you. Secondly, you can find this info in the DCE Online document here.

Struxureware Data Center Expert version 7.2 is available in the form of Open Virtualization Archive (.ova file). This .OVA file can be loaded on a virtual server. VMware ESXi 4.1.0 was used as the reference virtualization platform during the development of the StruxureWare Data Center Expert 7.2.4 virtual appliance, and is the first supported virtualization platform. You can use  the latest VMware ESXi OS for this Installation.

Vmware Server Configuration for installing DCE software as Virtual Appliance:

  • 4 core CPU
  • 16 GB RAM
  • 100 GB storage minimum(Please refer the below additonal disk note. Recommended to install the DCE with 10 GB first, and then add the additional hard disk with required storage space)
  • 1 GBPS LAN
  • Additional network adapter to enable private networking(Optional if the Customer wants to enable the Private Networking)

 Network Requirements for DCE:

 Customer must provide the MAC Address, IP Address, Subnet Mask and Default Gateway and hostname for StruxureWare Data Center Expert virtual appliance.

 A unique MAC Address is required for StruxureWare Data Center Expert . If the MAC Address originally assigned to the virtual appliance is changed, an error will occur on the primary interface, and the virtual appliance will not start. 

We can add one additional network adapter to enable private networking on DCE. You cannot

Remove a network adapter once it has been added.

  

Network Requirements : 

If the Customer wants to enable the DCE Private Networking to assign DHCP IP address to the PDUs on Private network, the Vmware Server Host needs to have the secondary Network. In this case, all the PDUs LAN cables need to be connected to the LAN Switch and then they need to be connected the Physical Private Network Adapter on the VMware Server Host.

 Procedure to add an additional network adapter on VM to enable Private Network:

 You can add one additional network adapter to enable private networking. You cannot

remove a network adapter once it has been added.

1. Gracefully shut down the virtual appliance.

2. Select the StruxureWare Data Center Expert virtual appliance, and select the option

to edit the virtual machine settings.

3. Select the options to add an ethernet adapter.

4. Specify the type and the network connection. Ensure this connection is mapped correctly, particularly when the DHCP server will be enabled on the private network interface.

5. Power on the virtual appliance.

6. In the console view, login to the virtual appliance using apcsetup as the username

and password.

7. Within five seconds, press m to modify the settings.

8. Accept the settings you configured previously, or modify settings if needed.

9. Press y to accept the Enable private network interface option.

10. Specify whether you want to enable the DHCP server on the private network interface.

 

Minimum System Requirements StruxureWare Data Center Expert console:

The StruxureWare Data Center Expert console is a stand-alone Java application that runs on systems that meet the following

requirements:

• A PC with a 1-GHz or better AMD/Intel processor running Microsoft® Windows® 2003 Server (SP2), Microsoft

Windows XP (SP1,SP2 or SP3), Windows Vista, or Windows 7, Red Hat® Enterprise Linux® version 5.0

• At least 1 GB of RAM

• Screen resolution should be set to at least 1024 x 768.

• Supported browsers: Microsoft Internet Explorer® 8, 9,10; Mozilla® Firefox® 17.0; Google Chrome™ 23.0

 

Adding disk space to a virtual appliance:


To increase storage for the virtual appliance, you must create additional hard disks.
You cannot change the size of an existing hard disk, or remove a hard disk once it has been
created. An error will occur on the primary interface, and the StruxureWare Data Center
Expert virtual appliance will not start.
1. Gracefully shut down the virtual appliance.
2. In your virtual server console, select the option to add a hard disk.
3. Choose the hard disk size.
See StruxureWare Data Center Expert virtual server equivalent configurations.
4. Choose thin or thick provisioning.
5. Power on the virtual appliance.

I am also sharing the screen shots of the DCE software OVA file deployment on VMware ESXi as one of the VM guest. This is not an official document. Its just for your reference. 

 

 

Regards,

Bala

 

 

(CID:110015157)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:53 AM . Last Modified: ‎2024-04-08 03:11 AM

0 Likes
0
1138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:53 AM . Last Modified: ‎2024-04-08 03:11 AM

Dear Shemil,

I have provided the following DCE Server requirements to one of the Customers. I am sharing the same to you. Secondly, you can find this info in the DCE Online document here.

Struxureware Data Center Expert version 7.2 is available in the form of Open Virtualization Archive (.ova file). This .OVA file can be loaded on a virtual server. VMware ESXi 4.1.0 was used as the reference virtualization platform during the development of the StruxureWare Data Center Expert 7.2.4 virtual appliance, and is the first supported virtualization platform. You can use  the latest VMware ESXi OS for this Installation.

Vmware Server Configuration for installing DCE software as Virtual Appliance:

  • 4 core CPU
  • 16 GB RAM
  • 100 GB storage minimum(Please refer the below additonal disk note. Recommended to install the DCE with 10 GB first, and then add the additional hard disk with required storage space)
  • 1 GBPS LAN
  • Additional network adapter to enable private networking(Optional if the Customer wants to enable the Private Networking)

 Network Requirements for DCE:

 Customer must provide the MAC Address, IP Address, Subnet Mask and Default Gateway and hostname for StruxureWare Data Center Expert virtual appliance.

 A unique MAC Address is required for StruxureWare Data Center Expert . If the MAC Address originally assigned to the virtual appliance is changed, an error will occur on the primary interface, and the virtual appliance will not start. 

We can add one additional network adapter to enable private networking on DCE. You cannot

Remove a network adapter once it has been added.

  

Network Requirements : 

If the Customer wants to enable the DCE Private Networking to assign DHCP IP address to the PDUs on Private network, the Vmware Server Host needs to have the secondary Network. In this case, all the PDUs LAN cables need to be connected to the LAN Switch and then they need to be connected the Physical Private Network Adapter on the VMware Server Host.

 Procedure to add an additional network adapter on VM to enable Private Network:

 You can add one additional network adapter to enable private networking. You cannot

remove a network adapter once it has been added.

1. Gracefully shut down the virtual appliance.

2. Select the StruxureWare Data Center Expert virtual appliance, and select the option

to edit the virtual machine settings.

3. Select the options to add an ethernet adapter.

4. Specify the type and the network connection. Ensure this connection is mapped correctly, particularly when the DHCP server will be enabled on the private network interface.

5. Power on the virtual appliance.

6. In the console view, login to the virtual appliance using apcsetup as the username

and password.

7. Within five seconds, press m to modify the settings.

8. Accept the settings you configured previously, or modify settings if needed.

9. Press y to accept the Enable private network interface option.

10. Specify whether you want to enable the DHCP server on the private network interface.

 

Minimum System Requirements StruxureWare Data Center Expert console:

The StruxureWare Data Center Expert console is a stand-alone Java application that runs on systems that meet the following

requirements:

• A PC with a 1-GHz or better AMD/Intel processor running Microsoft® Windows® 2003 Server (SP2), Microsoft

Windows XP (SP1,SP2 or SP3), Windows Vista, or Windows 7, Red Hat® Enterprise Linux® version 5.0

• At least 1 GB of RAM

• Screen resolution should be set to at least 1024 x 768.

• Supported browsers: Microsoft Internet Explorer® 8, 9,10; Mozilla® Firefox® 17.0; Google Chrome™ 23.0

 

Adding disk space to a virtual appliance:


To increase storage for the virtual appliance, you must create additional hard disks.
You cannot change the size of an existing hard disk, or remove a hard disk once it has been
created. An error will occur on the primary interface, and the StruxureWare Data Center
Expert virtual appliance will not start.
1. Gracefully shut down the virtual appliance.
2. In your virtual server console, select the option to add a hard disk.
3. Choose the hard disk size.
See StruxureWare Data Center Expert virtual server equivalent configurations.
4. Choose thin or thick provisioning.
5. Power on the virtual appliance.

I am also sharing the screen shots of the DCE software OVA file deployment on VMware ESXi as one of the VM guest. This is not an official document. Its just for your reference. 

 

 

Regards,

Bala

 

 

(CID:110015157)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 09:53 AM . Last Modified: ‎2023-10-22 04:14 AM

0 Likes
0
1138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 09:53 AM . Last Modified: ‎2023-10-22 04:14 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore