Posted: β2020-07-04 02:43 AM . Last Modified: β2024-04-05 03:44 AM
Hi all,
When I try to upload the newest Genome Library I get an error please see picture.
We upgraded to the newest version of the DCO yesterday on a new virtual machine.
Can someone help?

(CID:126185315)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 02:44 AM . Last Modified: β2024-04-05 03:44 AM
Hi Kenneth,
Many thanks for providing the data, specially the useful backup file. The master catalog appeared to be locked and therefore would not allow a manual update. Apparently there might have been some unsuccessful attempts sometime ago.
However, it is now unlocked and the "Fixed_...." backup file is ready for you to be downloaded from my box folder. After restoring this backup file, you should be able to apply your Genome updates.
Please let me know if you have questions or need instructions, thanks.
Kind regards
(CID:126185915)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 02:43 AM . Last Modified: β2024-04-05 03:44 AM
Hi Kenneth,
I've just tested Genome update on my 8.2 without any problem. I was wondering if it is possible to ask for the following data:
client application.log file (usually located in Win, C:\Users\
server logs, can be downloaded from webmin interface (StuxureWare DC Operation > Download Log Files > "Download log files")
and possibly a copy of the latest backup file
I will send you an invite to my =S= box shortly, in case if you would kindly share the data safely with me, thanks.
Kind regards
(CID:126185376)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 02:44 AM . Last Modified: β2024-04-05 03:44 AM
Hi Jef,
I have now provided the files as requested π
Thanks so far
(CID:126185495)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 02:44 AM . Last Modified: β2024-04-05 03:44 AM
Many thanks Kenneth,
I will have a look and get back to you as soon as possible,
Kind regards
(CID:126185519)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 02:44 AM . Last Modified: β2024-04-05 03:44 AM
Hi Kenneth,
Many thanks for providing the data, specially the useful backup file. The master catalog appeared to be locked and therefore would not allow a manual update. Apparently there might have been some unsuccessful attempts sometime ago.
However, it is now unlocked and the "Fixed_...." backup file is ready for you to be downloaded from my box folder. After restoring this backup file, you should be able to apply your Genome updates.
Please let me know if you have questions or need instructions, thanks.
Kind regards
(CID:126185915)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 02:44 AM . Last Modified: β2024-04-05 03:44 AM
Many Thanks Jeff,
It worked π
BR
Kenneth
(CID:126186361)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 02:44 AM . Last Modified: β2024-04-05 03:44 AM
Hi Kenneth,
You are most welcome - sounds great, many thanks for the update.
Kind regards
(CID:126186366)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 02:44 AM . Last Modified: β2023-10-22 04:13 AM