UPS firmware upgrade: Device Definition File (DDF) transfer failure

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • UPS firmware upgrade: Device Definition File (DDF) transfer failure
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:32 PM . Last Modified: ‎2024-04-08 12:56 AM

0 Likes
6
1548
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:32 PM . Last Modified: ‎2024-04-08 12:56 AM

UPS firmware upgrade: Device Definition File (DDF) transfer failure

Hi,

after upgrading UPS (Smart-UPS RT 2000 RM XL) firmware from v6.4.0 to v6.4.6 via DCE (7.4.1.5) and after via FW_Upgrade_R2 tool, the DCE shows this error message: " Device status may be inaccurate because an attempt to transfer a device definition file (DDF) failed."

To be noted that via SSH/console the UPS seems to be ok:  AOS and APP both upgraded to v6.4.6 and Stat: P+ N+ A+.

If "upgrading firmware files" were transferred properly, than this mean that this DCE error messages does not depend to scp, ssh, snmp, account and password.

 

Please advice.

Brgds,

Massimo  

(CID:116925087)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:33 PM . Last Modified: ‎2024-04-08 12:56 AM

0 Likes
2
1547
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:33 PM . Last Modified: ‎2024-04-08 12:56 AM

Hi Massimo,

 

K-base FA177004 talks about this issue. If you have used the firmware utility (as you mentioned, FW_Upgrade_R2 tool) for the upgrade, there is nothing here proving that SSH/SCP between DCE and the device are not having issues. DCE may not have the right settings or passwords. The network can also be blocking the correct protocol between the server and device while allowing it from the computer you used the FW_Upgrade_R2 tool on. 

 

If you check the release notes however, you will see the following under known issues on the recent DCE versions

PDF Library:

· APC SNMP Device Configuration File Transfer Using SCP Fails
File transfer using SCP fails on some APC SNMP devices with firmware lower than AOS v6.3.3. For best results, enable FTP on the device, and set the protocol to FTP Only in the “Device File Transfer Settings” display before you select the devices you want to update. Additionally, both SCP and FTP file transfer fails on all v6.x devices with touch screens (apc_hw06_aos_xxx). See the StruxureWare Data Center Expert documentation on http://dcimsupport.apc.com for the most recent information on APC SNMP Device Configuration.

 

Steve

(CID:116925100)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:33 PM . Last Modified: ‎2024-04-08 12:56 AM

In response to DCIM_Support
0 Likes
0
1547
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:33 PM . Last Modified: ‎2024-04-08 12:56 AM

Ciao Steven,

just finished to do some test:

  • upgrading DCE to v7.4.2 did not solve the problem; 
  • everything was fine using DIRECTLY and ONLY the "FW_Upgrade_R2" tool to upgrade the firmware of (another) UPS;

 

so the cause of problem seems to be the "Apply Firmware Update..." features of DCE using "scp only" as transfer method. 

 

Brgds,

Massimo

(CID:116925335)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:33 PM . Last Modified: ‎2024-04-08 12:55 AM

In response to DCIM_Support
0 Likes
0
1547
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:33 PM . Last Modified: ‎2024-04-08 12:55 AM

... Just noted that DCE v7.4.3 should solve DDF problems.

I've just requested this version.

 

NOTE: After a while also the second UPS showed the same problem.

 

brgds,

Massimo.

 

(CID:116925337)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:33 PM . Last Modified: ‎2024-04-08 12:55 AM

0 Likes
1
1547
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:33 PM . Last Modified: ‎2024-04-08 12:55 AM

Not sure if this is the case in your scenario but we have a few of our devices Firewalled and in order to get SCP  to work we have to allow PING protocol.  Looks like it pings the device first and if it gets a response it continues but if it gets no response then it fails.  just a thought...

 

Toby

 

(CID:116926385)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:33 PM . Last Modified: ‎2024-04-08 12:55 AM

In response to DCIM_Support
0 Likes
0
1547
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:33 PM . Last Modified: ‎2024-04-08 12:55 AM

Toby Bouzane, of course, is right about the ICMP-protocol, which is used, in particular, for the ping command.

After all, as far as I know, both the FW_Upgrade_R2 tool under MS Windows and the built-in device firmware update tools in the DCE-server operate the above protocol to determine the availability of devices after consecutive reboots (after the apc bootmon, apc aos and apc app components are updated).

With best regards.

(CID:116926434)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:33 PM . Last Modified: ‎2023-10-22 04:08 AM

0 Likes
0
1547
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:33 PM . Last Modified: ‎2023-10-22 04:08 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore