Trouble moving an empty rack

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Trouble moving an empty rack
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:54 PM . Last Modified: β€Ž2024-04-05 04:46 AM

0 Likes
17
2903
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:54 PM . Last Modified: β€Ž2024-04-05 04:46 AM

Trouble moving an empty rack

We recently moved some racks in our actual data center and are trying to mirror it in DCO. There are a few tiles in the grid though (a 2' x 6' area) that won't allow any racks to be placed, by moves or with new assets.

Anyone else run into a similar issue, or know a fix?

(CID:125212342)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:55 PM . Last Modified: β€Ž2024-04-05 04:46 AM

0 Likes
8
2903
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:55 PM . Last Modified: β€Ž2024-04-05 04:46 AM

Hi Austin,

Based on your kindly shared screen captures, it seems basically your Hot Aisle Containment System is not correctly configured. It seems your racks/row is overlapping the containment system, and not being included in the HACS.  Here is an illustration of Hot (and Cold) Aisle Containment system:

So I would basically check/correct the containment system first, and then it should be possible to move/relocate the rack(s).

Hope this helps,

Kind regards

(CID:125212880)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 17
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:54 PM . Last Modified: β€Ž2024-04-05 04:46 AM

0 Likes
6
2902
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:54 PM . Last Modified: β€Ž2024-04-05 04:46 AM

unlock the room, move the perforated floor tiles (use the mouse or select the perf tile and use the arrow keys) then move your racks. move the perf tiles to where they need to be, re-lock the room once you're done.

 

 If you have a hot or cold aisle, you may need to temporarily resize that so its smaller and can make changes to the rack layout.

if you're still having issues, please post a screenshot

(CID:125212356)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:54 PM . Last Modified: β€Ž2024-04-05 04:46 AM

In response to DCIM_Support
0 Likes
0
2903
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:54 PM . Last Modified: β€Ž2024-04-05 04:46 AM

No luck, even with extending aisles and moving in the way assets. The First picture is the room before making any changes. I can move assets, extend the rows, etc. But where that large X is shows up as red when dragging a rack (NC-13) over it. The furthest I can move it over is where it is sitting now. Same issue happens when trying to drag a brand new rack from the genome library as well.

(CID:125212379)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:55 PM . Last Modified: β€Ž2024-04-05 04:46 AM

In response to DCIM_Support
0 Likes
0
2902
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:55 PM . Last Modified: β€Ž2024-04-05 04:46 AM

that definitely seems odd, sounds like the client still thinks their are racks in that location.

 

i'd still make sure you shrink your hot aisle first, then extend the row and add the rack(s).  

 

What version of DCO are you using?  Have you tried removing row 5A, Click Save, clicking the Operations data center tab, then clicking back into edit data center tab? 

(CID:125212404)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:55 PM . Last Modified: β€Ž2024-04-05 04:46 AM

In response to DCIM_Support
0 Likes
0
2902
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:55 PM . Last Modified: β€Ž2024-04-05 04:46 AM

I'm running 8.1.0 right now. I've deleted/moved everything that's close to this location a few times, and tried playing with the row and hot-aisle sizing to see if that would do anything. And if I remove one of those empty racks, I can place the desired rack there, but then I still get the same issue of that 'no man's land' for any other racks.

(CID:125212412)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:55 PM . Last Modified: β€Ž2024-04-05 04:46 AM

In response to DCIM_Support
0 Likes
0
2903
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:55 PM . Last Modified: β€Ž2024-04-05 04:46 AM

I think it's a row capacity issue, try increasing the capacity to include more cabinets and
review row properties

(CID:125213085)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:55 PM . Last Modified: β€Ž2024-04-05 04:46 AM

In response to DCIM_Support
0 Likes
0
2903
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:55 PM . Last Modified: β€Ž2024-04-05 04:46 AM

How do you change row capacity? I don't think that's a setting I've used before.

The row allows for racks to be added though, just not in a select space (see the red X).

(CID:125213091)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:55 PM . Last Modified: β€Ž2024-04-05 04:46 AM

In response to DCIM_Support
0 Likes
0
2903
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:55 PM . Last Modified: β€Ž2024-04-05 04:46 AM

https://dcimsupport.apc.com/display/public/UADCO8x/StruxureWare+Data+Center+Operation%3A+Capacity

(CID:125213102)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:55 PM . Last Modified: β€Ž2024-04-05 04:46 AM

0 Likes
8
2904
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:55 PM . Last Modified: β€Ž2024-04-05 04:46 AM

Hi Austin,

Based on your kindly shared screen captures, it seems basically your Hot Aisle Containment System is not correctly configured. It seems your racks/row is overlapping the containment system, and not being included in the HACS.  Here is an illustration of Hot (and Cold) Aisle Containment system:

So I would basically check/correct the containment system first, and then it should be possible to move/relocate the rack(s).

Hope this helps,

Kind regards

(CID:125212880)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:55 PM . Last Modified: β€Ž2024-04-05 04:45 AM

In response to DCIM_Support
0 Likes
0
2902
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:55 PM . Last Modified: β€Ž2024-04-05 04:45 AM

Hi Jef,

 

Unfortunately, still no luck. I matched the sizing of the hot aisle to the picture above, but it still does not allow me to place racks in the gap. I can place as much as I want from NC-13 and all the way to the right, but cannot place anything to its left, regardless of row/HACS sizing.

(CID:125212959)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:55 PM . Last Modified: β€Ž2024-04-05 04:45 AM

In response to DCIM_Support
0 Likes
0
2902
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:55 PM . Last Modified: β€Ž2024-04-05 04:45 AM

Hi Austin,

Would it be possible to ask for a copy of your backup file, so I can take a look. I will send you an invite to my =S= box shortly, so the data can be shared safely with me, if it is okay with you, thanks.

Kind regards

(CID:125212971)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:55 PM . Last Modified: β€Ž2024-04-05 04:45 AM

In response to DCIM_Support
0 Likes
0
2903
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:55 PM . Last Modified: β€Ž2024-04-05 04:45 AM

Thanks Jef,

My email is in my profile if you would like communicate that way as well. Let me know what works best for you.

(CID:125212980)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:56 PM . Last Modified: β€Ž2024-04-05 04:45 AM

In response to DCIM_Support
0 Likes
0
2902
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:56 PM . Last Modified: β€Ž2024-04-05 04:45 AM

Hi Austin,

I have your email and I have also resend an invite (to my box), thanks.

Kind regards

(CID:125213273)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:56 PM . Last Modified: β€Ž2024-04-05 04:45 AM

In response to DCIM_Support
0 Likes
0
2902
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:56 PM . Last Modified: β€Ž2024-04-05 04:45 AM

Thank you, I look forward to your email.

(CID:125213541)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:56 PM . Last Modified: β€Ž2024-04-05 04:45 AM

In response to DCIM_Support
0 Likes
0
2902
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:56 PM . Last Modified: β€Ž2024-04-05 04:45 AM

Hi Austin,

Many thanks for providing the data. There is a very thin "Block" (1 mm in Depth) occupying the space, that is located just beside the rack "NC-13":

If I move the racks NC-13 and CORE02 plus the row ROW-5A to somewhere else, then the block is more visible/illustrative in 3D view:

If I remove the block, then the 'space' is free and can place any rack there:

Kind regards

(CID:126158540)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:56 PM . Last Modified: β€Ž2024-04-05 04:45 AM

In response to DCIM_Support
0 Likes
0
2902
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:56 PM . Last Modified: β€Ž2024-04-05 04:45 AM

Thanks Jef!

That did the trick and I can place the rack as needed.

(CID:126158551)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:56 PM . Last Modified: β€Ž2024-04-05 04:45 AM

In response to DCIM_Support
0 Likes
0
2900
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:56 PM . Last Modified: β€Ž2024-04-05 04:45 AM

You are most welcome, Austin

Sounds great, many thanks for the update.

Kind regards

(CID:126158886)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 11:56 PM . Last Modified: β€Ž2023-10-22 04:07 AM

0 Likes
0
2900
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 11:56 PM . Last Modified: β€Ž2023-10-22 04:07 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore