Transfer Of A Device Definition File (DDF) Failed

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Transfer Of A Device Definition File (DDF) Failed
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
112
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:35 PM . Last Modified: ‎2024-04-09 02:16 AM

0 Likes
14
8327
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:35 PM . Last Modified: ‎2024-04-09 02:16 AM

Transfer Of A Device Definition File (DDF) Failed

Hi All,

Recently I have installed 2 APC UPS model Smart-UPS 3000 to our comm-room and connected to DCE version 7.2.7. The DCE is showing critical error :" Device status may be inaccurate because an attempt to transfer a device definition file (DDF) failed."

Any idea to fix this? I have fully admin log in right to those devices.

Do I need to contact multivender to update DDF ?

 

Thanks,

Minh

(CID:104174462)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:35 PM . Last Modified: ‎2024-04-09 02:16 AM

0 Likes
2
8320
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:35 PM . Last Modified: ‎2024-04-09 02:16 AM

Minh,

Please reference knowledge base  article FA177004.  Contents of which are pasted below.

Issue:

StruxureWare Data Center Expert message "Device status may be inaccurate due to attempt to transfer DDF failed"

Product Line:

StruxureWare Data Center Expert
APC Networked Devices

Environment: 

StruxureWare Central / Data Center Expert any version
APC Networked Devices

Cause:

StruxureWare Data Center Expert uses device definition files (DDF) to understand what information to poll and how to format different information from discovered devices. During discovery of APC devices and after a firmware update of APC devices, the StruxureWare server will attempt to download DDF files from the device using FTP or SSH. If the server is unable to perform this transfer, you will see a message stating "Device status may be inaccurate due to attempt to transfer DDF failed".

Resolution:

Please be sure to enable FTP or SSH on the device itself. Make sure that any firewalls between StruxureWare and the affected device(s) are allowing the appropriate protocols and ports (20 for ftp and 21 for ssh). Also make sure that the appropriate user names, passwords, protocols, and ports are listed in StruxureWare under the device menu, SNMP device communication settings, and device file transfer settings. You can add or edit current listings. You can also create entries for ranges of devices as well as entries for specific devices.

 

Best Regards,

Cory

(CID:104174464)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 14
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:35 PM . Last Modified: ‎2024-04-09 02:16 AM

0 Likes
2
8321
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:35 PM . Last Modified: ‎2024-04-09 02:16 AM

Minh,

Please reference knowledge base  article FA177004.  Contents of which are pasted below.

Issue:

StruxureWare Data Center Expert message "Device status may be inaccurate due to attempt to transfer DDF failed"

Product Line:

StruxureWare Data Center Expert
APC Networked Devices

Environment: 

StruxureWare Central / Data Center Expert any version
APC Networked Devices

Cause:

StruxureWare Data Center Expert uses device definition files (DDF) to understand what information to poll and how to format different information from discovered devices. During discovery of APC devices and after a firmware update of APC devices, the StruxureWare server will attempt to download DDF files from the device using FTP or SSH. If the server is unable to perform this transfer, you will see a message stating "Device status may be inaccurate due to attempt to transfer DDF failed".

Resolution:

Please be sure to enable FTP or SSH on the device itself. Make sure that any firewalls between StruxureWare and the affected device(s) are allowing the appropriate protocols and ports (20 for ftp and 21 for ssh). Also make sure that the appropriate user names, passwords, protocols, and ports are listed in StruxureWare under the device menu, SNMP device communication settings, and device file transfer settings. You can add or edit current listings. You can also create entries for ranges of devices as well as entries for specific devices.

 

Best Regards,

Cory

(CID:104174464)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:35 PM . Last Modified: ‎2024-04-09 02:15 AM

In response to DCIM_Support
0 Likes
0
8320
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:35 PM . Last Modified: ‎2024-04-09 02:15 AM

Hi Cory,

 

Thanks for your amazing quick respond. Everything are work perfectly as should be. You save my day

Thank again for you respond.

Regards,

Minh

(CID:104174494)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:35 PM . Last Modified: ‎2024-04-09 02:15 AM

In response to DCIM_Support
0 Likes
0
8320
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:35 PM . Last Modified: ‎2024-04-09 02:15 AM

You're welcome.

(CID:104174495)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:36 PM . Last Modified: ‎2024-04-09 02:15 AM

0 Likes
5
8320
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:36 PM . Last Modified: ‎2024-04-09 02:15 AM

I am having the same problem with a 250kW unit. I have tried to FTP into the device and SSH into it and I can log in just fine. I also created an SNMP login just for this device and tried FTP and SCP options. I am not sure what SCP is though...

I have deleted and re-added the device several times with no luck. Any additional troubleshooting options?

Regards,

J

(CID:105471643)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:36 PM . Last Modified: ‎2024-04-09 02:15 AM

In response to DCIM_Support
0 Likes
0
8320
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:36 PM . Last Modified: ‎2024-04-09 02:15 AM

John, The error message indicates that the StruxureWare server is unable to pull a file off of the device called ddf.zip by either use FTP or SCP (Secure Copy), depending on how the network management card is configured. DCE uses the credentials to connect to the device, which are listed under: Device > SNMP Device Communication Settings > Device File Transfer Settings. The credentials may currently be applying to a range of values. Try adding a new setting to the screen that is specific to the IP address of this device with the admin credentials of the network management card. Right click on the device and then select Request Device Scan under the Device View pane. If it still does not come in, please ensure that the network has the appropriate ports open from the Data Center Expert server to the device. Regards, Cory

(CID:105471650)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:36 PM . Last Modified: ‎2024-04-09 02:15 AM

In response to DCIM_Support
0 Likes
0
8320
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:36 PM . Last Modified: ‎2024-04-09 02:15 AM

My issue still isn't fixed. However, I made progress. You mentioned it and I overlooked it, you need to enable FTP OR SCP. Not both. Once I did this, I rebooted the card and deleted the device in DCE. Then I re-scanned for the device. It found it with the same 'unable to retrieve DDF'. I checked the NMC log and it says in the log the file download failed twice and then on the third try "SSH/SCP: File Transfer Complete". But the alarm is still there. I clicked "Request Device Scan" and it didn't go away. Any other ideas?

(CID:105471859)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:36 PM . Last Modified: ‎2024-04-09 02:15 AM

In response to DCIM_Support
0 Likes
0
8320
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:36 PM . Last Modified: ‎2024-04-09 02:15 AM

You will need to make sure you have listed in the "Device File Transfer Settings" the FTP username & associated FTP password for the chosen devices are listed in the section found under the "Device" drop down in the DCE Client toolbar and then choose "SNMP Device Communication Settings" and then choose "Device Transfer Settings" then within the configuration box you will need to list all of the different logins & passwords for your devices.

(CID:105471996)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:36 PM . Last Modified: ‎2024-04-09 02:15 AM

In response to DCIM_Support
0 Likes
0
8320
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:36 PM . Last Modified: ‎2024-04-09 02:15 AM

I added the user for the device, which I logged into just fine. Even used an FTP program and accessed the device with no issues. You mention adding the FTP username and password? Where do you find the FTP username and password in the device? I see user accounts to access the device however nothing for an FTP user in the device.

(CID:105474233)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:36 PM . Last Modified: ‎2024-04-09 02:15 AM

In response to DCIM_Support
0 Likes
0
8320
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:36 PM . Last Modified: ‎2024-04-09 02:15 AM

the FTP user/password for the device is normally the same as the Admin user/password for the devices NMC (network management card) and you "add" this information in the DCE as I listed above. (so DCE knows what user/pass to use)

(CID:105474243)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:36 PM . Last Modified: ‎2024-04-09 02:15 AM

0 Likes
3
8320
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:36 PM . Last Modified: ‎2024-04-09 02:15 AM

My issue still isn't fixed. However, I made progress. You mentioned it and I overlooked it, you need to enable FTP OR SCP. Not both. Once I did this, I rebooted the card and deleted the device in DCE. Then I re-scanned for the device. It found it with the same 'unable to retrieve DDF'.

I checked the NMC log and it says in the log the file download failed twice and then on the third try "SSH/SCP: File Transfer Complete". But the alarm is still there. I clicked "Request Device Scan" and it didn't go away.

I tried just FTP only and I get the error "...unauthorized user attempting to access the FTP interface...". How do I make the DCE server, or the apc account authorized? I don't see any options.

Any other ideas?

(CID:105471951)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:36 PM . Last Modified: ‎2024-04-09 02:15 AM

In response to DCIM_Support
0 Likes
0
8319
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:36 PM . Last Modified: ‎2024-04-09 02:15 AM

I got fed up and changed out the Network Card. The unit HAD an AP9635CH and I swapped it for an AP9635. What is the difference?

(CID:105471972)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:36 PM . Last Modified: ‎2024-04-09 02:15 AM

In response to DCIM_Support
0 Likes
0
8319
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:36 PM . Last Modified: ‎2024-04-09 02:15 AM

The AP9635 and the AP9635CH card are the same Network Management Cards.

(CID:105471973)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:37 PM . Last Modified: ‎2024-04-09 02:15 AM

In response to DCIM_Support
0 Likes
0
8319
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:37 PM . Last Modified: ‎2024-04-09 02:15 AM

So I changed the card, which had an earlier (blue) GUI and everything worked great! I should have left it alone. Then I did the stupid thing and upgraded to the latest firmware which broke the card to DCE communication. I have a support ticket (#27583418) but the only solution is to send a tech out to "upgrade all the firmware on the UPS'. Which I don't think will fix the problem since the sypx v6.3.2 of the network card broke the system. What is the earlier version of the AP9635 card? So I can downgrade it? What changed in the firmware to break the network settings between DCE and the network card?

(CID:105472117)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:37 PM . Last Modified: ‎2023-10-31 11:39 PM

0 Likes
0
8319
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:37 PM . Last Modified: ‎2023-10-31 11:39 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore