Thumbnail issue with DCE 7.2x and NetBotz 5xx

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Thumbnail issue with DCE 7.2x and NetBotz 5xx
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:59 PM . Last Modified: ‎2024-04-09 01:36 AM

0 Likes
4
628
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:59 PM . Last Modified: ‎2024-04-09 01:36 AM

Thumbnail issue with DCE 7.2x and NetBotz 5xx

Hi All.NetBotz 550 with the new IP in DCE.png

In need of assistances with DCE and the NetBotz Rack Monitor Camera Pods.

I have an issue where I have change the network from 10.x.x.x to 192.x.x.x. Once we re-IP the endpoints DCE and the NetBotz appliances are up, but the Thumbnail view in the DCE surveillance tab doesn't detect any camera, the device view in DCE shows the camera pods listed under the NetBotz.

 

Subnet: changed from 10.0.0.0/24 to 192.168.0.0/24

NetBotz Rack Monitor 550 on 4.4.1

DCE on 7.2.7

 

From troubleshooting the issue, it seems to me that once the Camera Pod is added into DCE and then if the NetBotz IP changes,  DCE is ware of the NetBotz ip change but still references the Camera Pod using the previous hostname/ip address.

 

-I have upgrade the firmware on the NetBotz from 3.1 to 4.x,

-physically reset the netbotz

-tried using a different camera

 

Thx.

~Nit

c/-nitin.nand@non.schneider-electric.om

(CID:105459863)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:59 PM . Last Modified: ‎2024-04-09 01:35 AM

0 Likes
2
628
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:59 PM . Last Modified: ‎2024-04-09 01:35 AM

Hi Nitan,

 

Did you remove and re-add the NetBotz appliance from the DCE server?

Is the DCE server a hardware server or VM? If VM , how many NICs?

You stated you changed the IP from a 10.10 to a 192.168 address. Is that the public or private LAN?

If you changed the public LAN to 192.168, is the private LAN still set to 192.168? If so, that needs to be changed. Public and private should be set to different IP schemes. 

 

Steve

(CID:105459919)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:00 PM . Last Modified: ‎2024-04-09 01:35 AM

In response to DCIM_Support
0 Likes
0
628
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:00 PM . Last Modified: ‎2024-04-09 01:35 AM

Hi Steve. Yep.. the netbotz was removed and added back into the DCE server. the DCE is a OVA instance with a single NIC. Public LAN IP was changed to the 192.168.x.x range as well. I replicated the situation using a physical DCE server and the thumbnail survliance tab shows the camera.. soo. perhaps its something too do with the VM. I could delete the NIC and recreated it on the VMWare or generate a new MAC address to see if that helps to flush the pervious TCP settings. Re. Niti

(CID:105459962)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:00 PM . Last Modified: ‎2024-04-09 01:35 AM

In response to DCIM_Support
0 Likes
0
628
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:00 PM . Last Modified: ‎2024-04-09 01:35 AM

Hi Nitin, You may also want to add a free 5-node version to this same VM host. Add it there. If that works, you can also rule out it being something in the VM host blocking it and you'd be narrowing it down to the specific instance of DCE VM. Steve

(CID:105460148)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:00 PM . Last Modified: ‎2023-10-31 11:39 PM

0 Likes
0
628
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:00 PM . Last Modified: ‎2023-10-31 11:39 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore