Dear team,
Symmetra PX ups output current is L1-22A showing on its user display while i had checked physical with clamp meter which in 60Amp. Means L1-22Amp reading is incorrect, I have replaced it MIM/RIM for its rectification but this issue is still exist. Please tell guide is there any other step to rectify or its malfunctioning of Current Transformer.
Regards
MS
(CID:145850785)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 08:08 PM . Last Modified: 2024-04-03 01:19 AM
Dear Muhammad Shahzad,
I suspect, that this problem is related to the malfunction of the current transformer in phase L1. Six months ago, I had a similar problem.
Conclusion: You need to contact the =SE= local service center staff to replace defective parts in your UPS.
With respect.
(CID:147199137)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 08:08 PM . Last Modified: 2024-04-03 01:19 AM
Dear Muhammad Shahzad,
I suspect, that this problem is related to the malfunction of the current transformer in phase L1. Six months ago, I had a similar problem.
Conclusion: You need to contact the =SE= local service center staff to replace defective parts in your UPS.
With respect.
(CID:147199137)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 08:08 PM . Last Modified: 2024-04-03 01:19 AM
Thanks spezialist
(CID:147201660)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 08:09 PM . Last Modified: 2024-04-03 01:19 AM
Ok, very thanks for the good feedback 😀.
(CID:147201674)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 08:09 PM . Last Modified: 2023-10-22 04:05 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.