StruxureWare Server and Client Version Mismatch

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • StruxureWare Server and Client Version Mismatch
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 01:58 AM . Last Modified: β€Ž2024-04-05 03:58 AM

0 Likes
14
3030
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 01:58 AM . Last Modified: β€Ž2024-04-05 03:58 AM

StruxureWare Server and Client Version Mismatch

Hi

I keep getting a mismatch when trying to run SWC client.

The server version is 7.0.0.284 and I have rebooted it a few times.

I have also downloaded the software client directly from the server VM on different Windows computers.

I have verified that the downloaded client version is also 7.0.0.284

I am not connected via VPN.

Can anyone help? 

(CID:126177881)

Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • bug
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 01:59 AM . Last Modified: β€Ž2024-04-05 03:58 AM

0 Likes
1
3028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 01:59 AM . Last Modified: β€Ž2024-04-05 03:58 AM

Hi Steven Marchetti, Rana Ajmal, spezialist

I've got this resolved now. Turned out to be an SSL issue.

Thanks πŸ˜€ 

(CID:128065222)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 14
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 01:58 AM . Last Modified: β€Ž2024-04-05 03:58 AM

0 Likes
4
3028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 01:58 AM . Last Modified: β€Ž2024-04-05 03:58 AM

Hi Seun,

As noted in k-base FA158446, the version is the main issue but it has also been seen when using VPN and hostname (not FQDN). Have you tried by IP? Have you tried connecting from other systems?

Is your login using a local account or active directory/LDAP account? If so, it could be that DCE is not capable of reaching the remote authentication server. I know this latter issue is an incorrect error but I believe it may have been updated to show the correct error in newer versions.

 

 

Thanks,

Steve

(CID:126177888)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 01:58 AM . Last Modified: β€Ž2024-04-05 03:58 AM

In response to DCIM_Support
0 Likes
0
3028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 01:58 AM . Last Modified: β€Ž2024-04-05 03:58 AM

Hi Steve,

Thanks for your response. I am not using VPN however.

Also, I am not using hostname nor FQDN, but connecting via IP.

The login is via local account.

Thanks 

(CID:126178039)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 01:58 AM . Last Modified: β€Ž2024-04-05 03:58 AM

In response to DCIM_Support
0 Likes
0
3028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 01:58 AM . Last Modified: β€Ž2024-04-05 03:58 AM

Hi Seun,

did you try from another client? Have you tried Rana Ajmal s suggestion about the full uninstall?  What os are you running. Since this is 7.0 it has been running for some time. Is it a VM or hardware server? What, if anything, has changed? Do you have any backups? 

 

Steve. 

(CID:126178067)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 01:58 AM . Last Modified: β€Ž2024-04-05 03:58 AM

In response to DCIM_Support
0 Likes
0
3028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 01:58 AM . Last Modified: β€Ž2024-04-05 03:58 AM

Hi Steve,

  • Tried on 3x different clients (Windows 7 and 10 Pro)
  • I have done a full uninstall as per Rana Ajmals advice
  • Server is on a VM
  • The only thing that has changed was an upgrade. The previous server version was 6.x.x. This was upgraded to 7.0.0.284 and since then, there has been the server/client mismatch

Thanks

(CID:126178925)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 01:58 AM . Last Modified: β€Ž2024-04-05 03:58 AM

In response to DCIM_Support
0 Likes
0
3028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 01:58 AM . Last Modified: β€Ž2024-04-05 03:58 AM

Hi Seun,

Do you have a backup of the 6.x system. Your best option to return to a working version would likely be to restore to the 6.x version and try the upgrade again. 

As for version info, I believe 7.0 was the first available as a VM. If that is the case, then the system is either a hardware server or the upgrade was done in a hardware server then a backup brought over to a VM. 

 

Steve. 

(CID:126179507)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 01:59 AM . Last Modified: β€Ž2024-04-05 03:58 AM

0 Likes
5
3028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 01:59 AM . Last Modified: β€Ž2024-04-05 03:58 AM

Hi seun.feyisetan,

            kindly follow the below steps.

1) uninstall the previous SWC clients including current version.

2) Delete the ISXC folder from C drive  (C:\Users\user-name\.isxc)

 

3) Download and install new client from IP.

 

BR,

Rana Ajmal

(CID:126177995)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 01:59 AM . Last Modified: β€Ž2024-04-05 03:58 AM

In response to DCIM_Support
0 Likes
0
3028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 01:59 AM . Last Modified: β€Ž2024-04-05 03:58 AM

Hi Rana Ajmal,

Thanks for your response and the suggestion.

I have not yet tried this...plus, I am not back in the office / internal network until Monday. I would not want to go via VPN as that has its potential issues (k-base FA158446) as highlighted by Steven Marchetti.

So, will give this a shot on Monday when I can connect via local IP...fingers crossed.

Thanks

(CID:126178040)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 01:59 AM . Last Modified: β€Ž2024-04-05 03:58 AM

In response to DCIM_Support
0 Likes
0
3028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 01:59 AM . Last Modified: β€Ž2024-04-05 03:58 AM

Dear seun.feyisetan,

Have you solved your issue or not?

With respect.

(CID:126183368)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 01:59 AM . Last Modified: β€Ž2024-04-05 03:58 AM

In response to DCIM_Support
0 Likes
0
3028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 01:59 AM . Last Modified: β€Ž2024-04-05 03:58 AM

Hi spezialist, Not yet. I have raised it with APC and it seems the only thing to do now is to re-deploy the SWC server, which I want to do as a last resort. Have you got any ideas I can try before that please?

(CID:126183402)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 01:59 AM . Last Modified: β€Ž2024-04-05 03:58 AM

In response to DCIM_Support
0 Likes
0
3028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 01:59 AM . Last Modified: β€Ž2024-04-05 03:58 AM

Dear seun.feyisetan,

Unfortunately, I do not have any new ideas on this. I think Steven Marchetti recommendations for you are the most correct, i.e.:

...Your best option to return to a working version would likely be to restore to the 6.x version and try the upgrade again.

Most recently, the customer also had a problem with the old ISX Central server, which for some reason could not be updated (Update ISX Central 6.3.0 -> 7.0.0: nothing to update?). And the solution to this problem is similar, i.e. re-deploy the ISX Central server. This is a guaranteed solution to the problem.

Many thanks for the feedback.

With respect.

(CID:126183498)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 01:59 AM . Last Modified: β€Ž2024-04-05 03:58 AM

In response to DCIM_Support
0 Likes
0
3028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 01:59 AM . Last Modified: β€Ž2024-04-05 03:58 AM

Thanks spezialist, Rana Ajmal and Steven Marchetti. 

I think there is a backup of the 6.x.x system. I'll attempt the restore and upgrade again. 

Thanks

(CID:126184143)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 01:59 AM . Last Modified: β€Ž2024-04-05 03:58 AM

0 Likes
1
3029
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 01:59 AM . Last Modified: β€Ž2024-04-05 03:58 AM

Hi Steven Marchetti, Rana Ajmal, spezialist

I've got this resolved now. Turned out to be an SSL issue.

Thanks πŸ˜€ 

(CID:128065222)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 01:59 AM . Last Modified: β€Ž2024-04-05 03:58 AM

In response to DCIM_Support
0 Likes
0
3028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 01:59 AM . Last Modified: β€Ž2024-04-05 03:58 AM

Dear seun.feyisetan,

I.e., the above problem only occurred when the DCE-client was connecting via the HTTPS protocol?

I understand you correctly?

Many thanks for the feedback πŸ˜€.

(CID:128065246)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 02:00 AM . Last Modified: β€Ž2023-10-22 04:02 AM

0 Likes
0
3028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 02:00 AM . Last Modified: β€Ž2023-10-22 04:02 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore