Hi
After install Portal v1.3.2, there's nothing on Portal's webpage. Here's some screen shot.
When I open service.msc, can't start the "StruxureWare Portal" service.
Thanks


(CID:103585429)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 04:30 PM . Last Modified: 2024-04-09 02:47 AM
Hi Brenda,
As a quick test I would suggest to restart the workstation and wait a while (at least 15 min or so) and let the Portal services to start. Perhaps re-installation might also be an option to be tested.
However the most general contributing factors might be:
- Firewall, (might be preventing the installation or blocking ports)
- Following ports should not be blocked: StruxureWare Portal using port 8080 (default) and postgreqsl using port 5432
- Antivirus, (might be preventing the installation or start of service(s))
- Virus scan tools: excluding the “portal” and “postgresql” installation folders may be required
- The following Portal related services must be running: : "postgresql" and "StruxureWare Portal"
Hope this help,
Kind regards
(CID:103585434)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 04:30 PM . Last Modified: 2024-04-09 02:47 AM
Hi Brenda,
As a quick test I would suggest to restart the workstation and wait a while (at least 15 min or so) and let the Portal services to start. Perhaps re-installation might also be an option to be tested.
However the most general contributing factors might be:
- Firewall, (might be preventing the installation or blocking ports)
- Following ports should not be blocked: StruxureWare Portal using port 8080 (default) and postgreqsl using port 5432
- Antivirus, (might be preventing the installation or start of service(s))
- Virus scan tools: excluding the “portal” and “postgresql” installation folders may be required
- The following Portal related services must be running: : "postgresql" and "StruxureWare Portal"
Hope this help,
Kind regards
(CID:103585434)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 04:30 PM . Last Modified: 2024-04-09 02:47 AM
Hi Jef, I turn off McAfee's firewall, then re-install , and start the portal service manually according the troubleshooting guide. It's working fine now. Thank you!
(CID:103585566)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 04:30 PM . Last Modified: 2024-04-09 02:47 AM
Hi Brenda, Well done! many thanks for getting back and sharing the good news. Kind regards
(CID:103585576)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 04:30 PM . Last Modified: 2023-10-31 11:37 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.