Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 11:25 AM . Last Modified: 2024-04-10 12:34 AM
Is the battery waring based on the install date or % of the rated battery capacity?
(CID:94603477)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 11:26 AM . Last Modified: 2024-04-10 12:33 AM
Smart UPS normally performs the Self Test to check the battery health at Start up and every 14 days by default. The self-test process compares the battery voltage during a discharge to an internal bad-battery template – basically, it places a load on the battery and measures the voltage drop. If the drop is too large for the given load, then the voltage will be beneath the failure level and the self-test will fail.
The below K-base document has got more information on the battery warning or replace battery warning:
http://www.apc.com/site/support/in/en/faq/
K-base ID: FA156584
It is also normally recommended to replace the VRLA type battery if the battery is more than 3 years old.
(CID:95354902)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 11:26 AM . Last Modified: 2023-10-31 11:35 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.