New DCE user here:
This latest version of the DDL (v.5) reports data down to the branch circuit level.
We've noticed that Breaker Phase Current reporting is off by a factor of 10. - eg. It's reporting 90A phase current, when it should be reporting 9.0A. This is consistent for each phase.
If there'a a better place to report this kind of bug, please let me know.
(CID:100340425)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 02:59 PM . Last Modified: 2024-04-09 04:00 AM
Hi John,
3rd party DDF files are created and maintained by a group at the following e-mail address:
Usually, to create a DDF they request a MIB and an SNMPwalk. They may request this again but if you have information such as screenshot showing the invalid format within DCE and where it is showing correctly, they should be able to correct it easily.
Thanks,
Steve
(CID:100340427)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 02:59 PM . Last Modified: 2024-04-09 04:00 AM
Hi John,
3rd party DDF files are created and maintained by a group at the following e-mail address:
Usually, to create a DDF they request a MIB and an SNMPwalk. They may request this again but if you have information such as screenshot showing the invalid format within DCE and where it is showing correctly, they should be able to correct it easily.
Thanks,
Steve
(CID:100340427)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 02:59 PM . Last Modified: 2024-04-09 04:00 AM
Thanks Steve, email sent to multivendor support.
(CID:100340445)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 02:59 PM . Last Modified: 2023-10-31 11:34 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.