Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Saving NEtbotz 755 video to a Windows share

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Saving NEtbotz 755 video to a Windows share
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
160
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
Dave-NotThatDave
Dave-NotThatDave
Explorer

Posted: ‎2024-07-05 11:28 AM

1 Like
6
2370
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-05 11:28 AM

Saving NEtbotz 755 video to a Windows share

Hi, we used to have a netbotz 450 which we replaced with a 755.  I can't seem to find documentation on how to save video to a Windows share.

 

Goal: Have the camera detect motion and then save 10 seconds of motion capture video to a Windows share.

Thanks

Labels
  • Labels:
  • Data Center Expert
  • Data Center Operation
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
APC_Steve
APC_Steve Leader
Leader

Posted: ‎2024-07-09 04:39 AM

0 Likes
5
2337
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-09 04:39 AM

Hi @Dave-NotThatDave ,


Sorry to be the bearer of bad news but this is one of the features that was not carried over from the older units to the new 700 series. The 750/755 NetBotz do not have the ability to save to a shared drive. The botz can e-mail and they can send alerts to Data Center Expert. The only workaround I can see is that if you have only the 1 755, you can set up a trial VM and alerts and surveillance can be sent to DCE.
OVA URL: https://download.struxureon.com/dce/VM/811/index.html

Sorry for the inconvenience.

Thanks,

Steve.

Reply

Link copied. Please paste this link to share this article on your social media post.

Dave-NotThatDave
Dave-NotThatDave
Explorer

Posted: ‎2024-07-09 07:46 AM

In response to APC_Steve
0 Likes
4
2310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-09 07:46 AM

There appears to be the ability to save to a SAMBA share?  Would that be saving to Linux, or something else?  I'm not familiar with SAMBA.  
And if that's not an option, we can save to a local SD card, correct?

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

APC_Steve
APC_Steve Leader
Leader

Posted: ‎2024-07-11 04:54 AM

In response to Dave-NotThatDave
0 Likes
3
2296
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-11 04:54 AM

Hi @Dave-NotThatDave ,

 

No, there is no ability to save to a local SD card on the NetBotz itself. The 700 series does have an internal SD card but that should only be accessible if you take the unit apart (unsupported and voids warranty). As for the samba share, I'm unsure where you're seeing this as an option in the NetBotz.


If you're referring to the camera itself, we've never offered these options as we only support use of the camera through connection to the NetBotz itself. Making changes in the camera can cause issues (although this one would not appear to interfere with anything NetBotz related). We only officially support use through the NetBotz appliance. Please also note that the camera should probably be on the public LAN to even attempt the samba option. Again, it's not supported from the NetBotz UI so we don't fully support it so if you try an SD card or a network share and it interferes with the connectivity to the NetBotz itself, we'll ask that you reset the camera back to defaults and won't be able to troubleshoot otherwise.

Steve

Reply

Link copied. Please paste this link to share this article on your social media post.

APC_Steve
APC_Steve Leader
Leader

Posted: ‎2024-07-11 12:23 PM

In response to APC_Steve
0 Likes
0
2288
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-11 12:23 PM

Hi @Dave-NotThatDave ,

I also wanted to note this from the camera's install guide:

https://download.schneider-electric.com/files?p_Doc_Ref=990-5974&p_enDocType=Quick+start+guide&p_Fil...

 

APC_Steve_0-1720725789158.png

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Dave-NotThatDave
Dave-NotThatDave
Explorer

Posted: ‎2024-07-11 01:16 PM

In response to APC_Steve
0 Likes
1
2271
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-11 01:16 PM

You can see below that there's configuration settings for file storage and motion detection and saving to NAS or SD Card or a SAMBA share.

DaveNotThatDave_0-1720728206056.png

DaveNotThatDave_3-1720728862396.png

 

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

APC_Steve
APC_Steve Leader
Leader

Posted: ‎2024-07-15 04:17 AM

In response to Dave-NotThatDave
0 Likes
0
2234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-07-15 04:17 AM

Hi @Dave-NotThatDave , Yes, I understand and I have seen that. and I won't answer again in the future just in case you're looking for a non-Schneider answer but I'll say again, making these changes is not supported as it is designed to work through the NetBotz 750/755. These changes are unsupported and sadly, we can't assist here.

 

Steve

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore