SOLVED: DCE can't assign APC Secure Interface (ASI) for ATS AP7723?

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • SOLVED: DCE can't assign APC Secure Interface (ASI) for ATS AP7723?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
127
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-02 05:12 PM . Last Modified: β€Ž2024-04-09 02:32 AM

0 Likes
6
1320
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-02 05:12 PM . Last Modified: β€Ž2024-04-09 02:32 AM

SOLVED: DCE can't assign APC Secure Interface (ASI) for ATS AP7723?

Hi all!

Problem essence: in some ATS devices (for example in three of ten) for the unclear reasons it is impossible to setup the IP address of the server DCE in so-called section [SecureInterface]. And some methods of setup were tested.

  1. This setup has to be performed automatically at detection of the device on the server DCE: it isn't setup, result negative, priority scanning at alarm doesn't become.
  2. It is possible to register server DCE manually in device "config.ini" with the subsequent loading of this file, for example: 

    [SecureInterface] ; APC Secure Interface (ASI): ; To add an ASI trap recipient, list the IP address in the following form: ; :, ; CurrentASISubscriber=192.168.0.1 ; To remove an ASI trap recipient, list the IP or DNS name using the keyword: ; RemoveASISubscriber=192.168.0.2 ; To remove all ASI trap recipients, use the keyword, value pair: ; RemoveALLASISubscribers=yes Access=disabled AuthenticationPhrase=APC ASI auth phrase EncryptionPhrase=APC ASI crypt phrase TrapPort=9952 CurrentASISubscriber=192.168.0.1:162, ISX Manager

    The last line is that that is necessary for us. But after reboot of the device the last line simply disappears and "CurrentASISubscriber" doesn't remain.

  3. It is possible to register manually above the specified setup by means of the "snmpset" command as it and does the DCE server, for example: 

    # snmpset -v2c -cprivate 192.168.0.130 .1.3.6.1.4.1.318.1.4.4.3.0 s "192.168.0.1:162,4" Error in packet. Reason: (genError) A general failure occured Failed object: SNMPv2-SMI::enterprises.318.1.4.4.3.0

    And in reply we receive here such mistake (therefore, it isn't strange that the DCE server can't make self this ASI-setup of the priority scanning device).

From all set of our devices of production APC for the unclear reasons such problem arose only on a quarter of devices, and, any sequence isn't observed. I.e., the reasons of emergence of this problem for me are a riddle...
Here the list of devices on which such ASI-problem was found:

  • ATS AP7721 (only some devices of this model were ASI-problem);
  • ATS AP7723 (only some devices of this model were ASI-problem);
  • NetBotz 200 (all devices of this model were ASI-problem);
  • PDPM277H (all devices of this model were ASI-problem);
  • Symmetra 160K (0G-9354) (only some devices of this model were ASI-problem);
  • Symmetra 48K (0G-9354) (only some devices of this model were ASI-problem);
  • Smart-UPS 1500 (AP9619) (all devices of this model were ASI-problem);
  • rPDU AP7857 (all devices of this model were ASI-problem).

     

And all devices have __ actual __ at the moment (November, 2015) the version of a microcode (online search and installation of updatings it was made by means of the DCE servers). And once again I will remind, that the ASI-problem wasn't solved by neither reboot, nor a poweroff/poweron of devices or resetting of their settings on factory default in any way.

SOLUTION:

The solution appeared very simple: in the configuration file of the ASI-problem device in section [SecureInterface] it is necessary to add the line "RemoveALLASISubscribers=yes" with the subsequent reboot of the device. Only after that it is possible to register successfully the IP address of the server DCE, and any of three below the specified ways:

  1. in the standard way, in the way of new search of the ASI-problem device on the DCE server (with the marked checkbox of priority scanning);

  2. manually, having stated in the configuration file in section [SecureInterface] the necessary IP address DCE server as it is described in a manual;

  3. manually, by means of the "snmpset" command as it does the DCE server, i.e. having emulated operations of the DCE server.

The last way most simple and interesting, therefore I will give an example for acquaintance.

  1. Initially, after reboot of the ASI-problem device with the option "RemoveALLASISubscribers=yes" we have no hidden trap receiver, i.e. any of the registered DCE server: 

    # snmpwalk -v2c -cpublic 192.168.0.139 .1.3.6.1.4.1.318.1.4.4.2 SNMPv2-SMI::enterprises.318.1.4.4.2 = No Such Object available on this agent at this OID
  2. Now we add as the hidden trap receiver the DCE server with the IP address 192.168.0.1 (actually, the DCE server executes similar command): 

    # snmpset -v2c -cprivate 192.168.0.139 .1.3.6.1.4.1.318.1.4.4.3.0 s "192.168.0.1:162,4" SNMPv2-SMI::enterprises.318.1.4.4.3.0 = STRING: "192.168.0.1:162,4"
  3. We check success of the executed command and we are convinced that now the server DCE is added and everything normally works: 

    # snmpwalk -v2c -cpublic 192.168.0.139 .1.3.6.1.4.1.318.1.4.4.2 SNMPv2-SMI::enterprises.318.1.4.4.2.1.1.1 = INTEGER: 1 SNMPv2-SMI::enterprises.318.1.4.4.2.1.2.1 = STRING: "192.168.0.1:162" SNMPv2-SMI::enterprises.318.1.4.4.2.1.3.1 = INTEGER: 4 SNMPv2-SMI::enterprises.318.1.4.4.2.1.4.1 = INTEGER: 0
  4. Similarly we add our second DCE server with the IP address 192.168.0.2: 

    # snmpset -v2c -cprivate 192.168.0.139 .1.3.6.1.4.1.318.1.4.4.3.0 s "192.168.0.2:162,4" SNMPv2-SMI::enterprises.318.1.4.4.3.0 = STRING: "192.168.0.2:162,4"
  5. Also we check result, being in parallel convinced that now we have in the list two DCE servers (as much as possible them can be to four): 

    # snmpwalk -v2c -cpublic 192.168.0.139 .1.3.6.1.4.1.318.1.4.4.2 SNMPv2-SMI::enterprises.318.1.4.4.2.1.1.1 = INTEGER: 1 SNMPv2-SMI::enterprises.318.1.4.4.2.1.1.2 = INTEGER: 2 SNMPv2-SMI::enterprises.318.1.4.4.2.1.2.1 = STRING: "192.168.0.1:162" SNMPv2-SMI::enterprises.318.1.4.4.2.1.2.2 = STRING: "192.168.0.2:162" SNMPv2-SMI::enterprises.318.1.4.4.2.1.3.1 = INTEGER: 4 SNMPv2-SMI::enterprises.318.1.4.4.2.1.3.2 = INTEGER: 4 SNMPv2-SMI::enterprises.318.1.4.4.2.1.4.1 = INTEGER: 0 SNMPv2-SMI::enterprises.318.1.4.4.2.1.4.2 = INTEGER: 0

    Right there it is possible to view the configuration file of our device and to be convinced that at section [SecureInterface] also there are two similar records with IP addresses of our DCE servers. I.e. that we also achieved :-).

     

  6. Now we will check, whether our DCE servers from the list of the hidden trap receivers are removed and we will execute here such command as it and does the DCE server: 

    # snmpset -v2c -cprivate 192.168.0.139 .1.3.6.1.4.1.318.1.4.4.3.0 s "192.168.0.2:162,2" SNMPv2-SMI::enterprises.318.1.4.4.3.0 = STRING: "192.168.0.2:162,2"
  7. Further we check and we are convinced that the server with the IP address 192.168.0.2 is already not present: 

    # snmpwalk -v2c -cpublic 192.168.0.139 .1.3.6.1.4.1.318.1.4.4.2 SNMPv2-SMI::enterprises.318.1.4.4.2.1.1.1 = INTEGER: 1 SNMPv2-SMI::enterprises.318.1.4.4.2.1.2.1 = STRING: "192.168.0.1:162" SNMPv2-SMI::enterprises.318.1.4.4.2.1.3.1 = INTEGER: 4 SNMPv2-SMI::enterprises.318.1.4.4.2.1.4.1 = INTEGER: 0
  8. Similarly we delete from the list the last from DCE servers with the IP address 192.168.0.1 with this commands: 

    # snmpset -v2c -cprivate 192.168.0.139 .1.3.6.1.4.1.318.1.4.4.3.0 s "192.168.0.1:162,2" SNMPv2-SMI::enterprises.318.1.4.4.3.0 = STRING: "192.168.0.1:162,2"
  9. And further simply we check and we are convinced that now on our device it isn't registered any hidden trap receiver: 

    # snmpwalk -v2c -cpublic 192.168.0.139 .1.3.6.1.4.1.318.1.4.4.2 SNMPv2-SMI::enterprises.318.1.4.4.2 = No Such Object available on this agent at this OID

That's it and very thanks for the support :-).

P.S.: after all, I found the solution of this ASI-problem earlier than an paid official support service of APC by Schneider Electric :-). Really I only who dealt with such unique and anybody yet not found ASI-problem?..

(CID:104173592)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-02 05:13 PM . Last Modified: β€Ž2024-04-09 02:32 AM

0 Likes
2
1319
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-02 05:13 PM . Last Modified: β€Ž2024-04-09 02:32 AM

Thank you for letting us know about the left alignment in the code block. I don't know why it does that, but we are looking into it πŸ™‚

(CID:104173960)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-02 05:13 PM . Last Modified: β€Ž2024-04-09 02:32 AM

0 Likes
0
1319
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-02 05:13 PM . Last Modified: β€Ž2024-04-09 02:32 AM

Hi spezialist - thanks for sharing πŸ™‚

(CID:104173698)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-02 05:13 PM . Last Modified: β€Ž2024-04-09 02:32 AM

0 Likes
0
1319
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-02 05:13 PM . Last Modified: β€Ž2024-04-09 02:32 AM

It is very pleasant to be useful to community :-).

Since the beginning of 2013 I have a quantity of various useful information and practical decisions on DCE. Therefore, I will also try further the most interesting to publish for a public review here.

P.S.: Stine, at me it is impossible to format with left alignment the text in code blocks in any way :-(. When editing code block everything looks ideally (left alignment), and after saves for some reason there is an center alignment of the text. Why? Very thanks for the support.

(CID:104173961)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-02 05:13 PM . Last Modified: β€Ž2024-04-09 02:32 AM

0 Likes
2
1320
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-02 05:13 PM . Last Modified: β€Ž2024-04-09 02:32 AM

Thank you for letting us know about the left alignment in the code block. I don't know why it does that, but we are looking into it πŸ™‚

(CID:104173960)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-02 05:13 PM . Last Modified: β€Ž2024-04-09 02:32 AM

In response to DCIM_Support
0 Likes
0
1319
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-02 05:13 PM . Last Modified: β€Ž2024-04-09 02:32 AM

πŸ™‚ Stine, and I here several times changed formatting and quitted nothing! Well though it is pleasant that I helped to find one more bug :-).

Stine, please, tell me please when this bug is corrected. Very thanks for the support.

(CID:104173964)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-02 05:13 PM . Last Modified: β€Ž2024-04-09 02:32 AM

In response to DCIM_Support
0 Likes
0
1318
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-02 05:13 PM . Last Modified: β€Ž2024-04-09 02:32 AM

Sorry to hear that. I will let you know when it is corrected πŸ™‚

(CID:104173965)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-02 05:13 PM . Last Modified: β€Ž2023-10-31 11:36 PM

0 Likes
0
1320
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-02 05:13 PM . Last Modified: β€Ž2023-10-31 11:36 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore