SNMP Trap Network Traffic for 200 device

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • SNMP Trap Network Traffic for 200 device
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
127
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:51 PM . Last Modified: ‎2024-04-09 04:04 AM

0 Likes
3
756
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:51 PM . Last Modified: ‎2024-04-09 04:04 AM

SNMP Trap Network Traffic for 200 device

Dear All,
 

I would like to know  How much network traffic occur when DCE communicate with infrastructure device such as rack PDUs, Sensors, UPS etc for 200 device in the network. 

Regards,

Emre Koca

(CID:100340138)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:52 PM . Last Modified: ‎2024-04-09 04:04 AM

0 Likes
0
756
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:52 PM . Last Modified: ‎2024-04-09 04:04 AM

Edit: I just realized you asked about DCE. My DCE server is averaging around 17.5Mbps with peaks up to 32.5Mbps. However there are dips to 2.5Mbps, so it is all over the place.

____

My DCO server which is running and connecting 2000+ devices with DCE sits mostly at 1Mbps with really short peaks at 9-10 Mbps as I am logging in, saving, etc.

 

Also, I did do a scan on a PDU and you can see the answer here:

Hope that helps.

J

 

(CID:100340152)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:51 PM . Last Modified: ‎2024-04-09 04:04 AM

0 Likes
0
756
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:51 PM . Last Modified: ‎2024-04-09 04:04 AM

Hi emrekoca,

 

Sorry but we do not have this information. When an APC device alerts, it sends a trap to DCE. We may be able to get the size of this. DCE will then (again only for an APC device) poll the device. Depending on the device and number of sensors, this poll may be a few k or 10 times that. It will be different for every device. If a non-APC device sends a trap, we do not do anything with the device, we only poll on schedule.

 

DCE will then do what it is configured to do. This could be an e-mail, short e-mail, send it's own trap, etc. This too will always be different depending on the actions, number of actions in a profile, profile configuration, etc.


Steve

(CID:100340147)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:52 PM . Last Modified: ‎2024-04-09 04:04 AM

0 Likes
0
757
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:52 PM . Last Modified: ‎2024-04-09 04:04 AM

Edit: I just realized you asked about DCE. My DCE server is averaging around 17.5Mbps with peaks up to 32.5Mbps. However there are dips to 2.5Mbps, so it is all over the place.

____

My DCO server which is running and connecting 2000+ devices with DCE sits mostly at 1Mbps with really short peaks at 9-10 Mbps as I am logging in, saving, etc.

 

Also, I did do a scan on a PDU and you can see the answer here:

Hope that helps.

J

 

(CID:100340152)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:52 PM . Last Modified: ‎2023-10-31 11:35 PM

0 Likes
0
756
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:52 PM . Last Modified: ‎2023-10-31 11:35 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore