Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

SNMP Device Scan Settings Priority Scanning with Netbotz 200

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • SNMP Device Scan Settings Priority Scanning with Netbotz 200
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 05:08 PM . Last Modified: ‎2024-04-05 12:01 AM

0 Likes
8
2094
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:08 PM . Last Modified: ‎2024-04-05 12:01 AM

SNMP Device Scan Settings Priority Scanning with Netbotz 200

The Priority scanning doesn't appear to work with the netbotz 200.

I have configured snmp traps to the dce server (7.5.0), but alerts only appear at the next poll interval (set to 5 minutes).

Other devices configured for Priority Scanning alert from DCE withing seconds rather than at the next poll.

Is this a limitation of the netbotz 200's? 

 

There is a trap test function on the netbotz, but no way to see if it was received by DCE.

(CID:130682085)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 05:08 PM . Last Modified: ‎2024-04-05 12:01 AM

0 Likes
0
2094
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:08 PM . Last Modified: ‎2024-04-05 12:01 AM

Dear Mark,

For me this is a long-known problem, the solution of which I know, but I do not know the reasons for its occurrence 😀. The solution to this problem can be found in my post .

To begin with, I highly recommend that you download the config.ini file from your problematic device and examine its section [SecureInterface]. Is there an IP-address for your target DCE-server in this section?

I will be interested in your answer.

With respect.

(CID:130682250)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 05:08 PM . Last Modified: ‎2024-04-05 12:01 AM

0 Likes
0
2094
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:08 PM . Last Modified: ‎2024-04-05 12:01 AM

Thanks for the response.

 

I didn't do the initial DCE server setup and devices have only been manually added since.

 

So does access disabled in this mean it is turned off ?

The CurrentAISubscriber is correct.

is the TrapPort the source or destination port? there are firewalls in the network between these.

 

My other Netbotz 200 appears to do the traps as notifications are fast.

There are two more Netbotz 250's that are also not working as expected.

 

Mark.

 

 

[SecureInterface]
; APC Secure Interface (ASI): 
; To add an ASI trap recipient, list the IP address in the following form:
; :,
; CurrentASISubscriber=192.168.0.1
; To remove an ASI trap recipient, list the IP or DNS name using the keyword:
; RemoveASISubscriber=192.168.0.2
; To remove all ASI trap recipients, use the keyword, value pair:
; RemoveALLASISubscribers=yes
Access=disabled
AuthenticationPhrase=APC ASI auth phrase
EncryptionPhrase=APC ASI crypt phrase
TrapPort=9952
CurrentASISubscriber=192.168.1.53:162, ISX Manager

(CID:130682864)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 05:08 PM . Last Modified: ‎2024-04-05 12:01 AM

0 Likes
0
2094
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:08 PM . Last Modified: ‎2024-04-05 12:01 AM

Dear Mark,

Judging by your config.ini, you are all set up correctly, because only one line is important for this:

CurrentASISubscriber=192.168.1.53:162, ISX Manager

All other lines in your case do not matter.

My other Netbotz 200 appears to do the traps as notifications are fast.

I.e., all your NetBotz-200 devices already work correctly with priority scanning? I.e., do all of your NetBotz-200 devices have the above line in the config.ini file? Did I understand you correctly?

There are two more Netbotz 250's that are also not working as expected.

I want to note, that NetBotz-200 and NetBotz-250 are very different devices from different generations. And yet, did you check the config.ini files for the presence of the above line for all your NetBotz-250 devices of the new generation?

With respect.

(CID:130682980)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 05:08 PM . Last Modified: ‎2024-04-05 12:01 AM

0 Likes
0
2094
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:08 PM . Last Modified: ‎2024-04-05 12:01 AM

Hi Spezialist,

Many thanks for your expert help.

With guidance from you posts on sorting this with an ATS, and inspecting the config.ini, I seem to have it working better on at least one. They all monitor generators via dry contacts, so I have to wait until a scheduled test to see if it has changed. An snmp set is an easy way to get the entry in. 

One thing that isn't configured on most of my devices is snmp writes. Enabling this and adding snmp trap entries enabled priority scanning for APC UPS's, but not the netbotz.

 

Thanks again,

 

Mark.

 

(CID:131336984)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 05:08 PM . Last Modified: ‎2024-04-05 12:01 AM

0 Likes
0
2094
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:08 PM . Last Modified: ‎2024-04-05 12:01 AM

Dear Mark,

It's nice to hear that it helped you 😀.

One thing that isn't configured on most of my devices is snmp writes. Enabling this and adding snmp trap entries enabled priority scanning for APC UPS's, but not the netbotz.

I do not understand why you can not do with NetBotz devices. I, for example, have no problems with NetBotz-200 devices.

Concerning the NetBotz-250 devices I can not say anything: these are devices of another generation. Therefore, you need to first clarify with which NetBotz devices you have problems?

With respect.

(CID:131337097)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 05:08 PM . Last Modified: ‎2024-04-05 12:01 AM

0 Likes
0
2094
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:08 PM . Last Modified: ‎2024-04-05 12:01 AM

Both Netbotz 200 and 250. Chnages have been made and I'll have them all tested again in the next few weeks.

 

(CID:131959240)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 05:09 PM . Last Modified: ‎2024-04-05 12:01 AM

0 Likes
0
2094
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:09 PM . Last Modified: ‎2024-04-05 12:01 AM

Dear Mark,

Tell us, please, could you solve your problem or not?

With respect.

(CID:131962922)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 05:09 PM . Last Modified: ‎2023-10-22 03:49 AM

0 Likes
0
2094
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 05:09 PM . Last Modified: ‎2023-10-22 03:49 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore