Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

SNMP Device Configuration - Master template?

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • SNMP Device Configuration - Master template?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
160
Jef
Jef Leader
114
gsterling
gsterling Mentor
79
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:00 PM . Last Modified: ‎2024-04-03 02:48 AM

0 Likes
4
1639
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:00 PM . Last Modified: ‎2024-04-03 02:48 AM

SNMP Device Configuration - Master template?

Hello all,

 

We manage a significant amount of APC devices via DCE and are utilizing the SNMP mass configuration more and more.

 

What I would like to is have one (or a few) "master" templates that have common settings for all our devices.  But the issue I'm running into is that those settings seem to be "named" different things on different devices and/or different firmware versions.

One example is Web Access:

 - In template A (from device A), there are two "fields": HTTP Access and HTTPS access

 - In template B (from device B), there is one field for the same setting: Web Protocol

 

Is it possible to create a master template that has all of the above settings included?  In this case, I would want it to have the following settings:

HTTP Access: Disable

HTTPS Access: Enable

Web Protocol: HTTPS

 

(CID:143264976)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:00 PM . Last Modified: ‎2024-04-03 02:48 AM

0 Likes
2
1638
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:00 PM . Last Modified: ‎2024-04-03 02:48 AM

Hi Martin,

 

The way to do this when choosing to configure devices directly (not from a template) is to select multiple devices and when looking at the device settings, uncheck the box to show shared settings only :

When you apply such a configuration however, you will receive errors as some values will not be able to get set on some devices. Pretty much every device should error in this configuration.

 

When creating a template however, you must create that template based on an individual device. Here I created one based on an older device with 3.9.1 firmware and I have the web access option:

Here, I chose a newer NMC and have the other options:

Since there is no option to choose multiple devices for creating a template, you can not have both options in the resulting template. Currently there is no way around this through DCE.

If this configuration on a single push is an absolute necessity, you could use the config.ini utility outside of DCE and manually edit the ini you're pushing to include all required values. This may be a little more effort though than pushing 2 different templates from DCE.

 

Thanks,

Steve

 

 

 

(CID:143755127)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:00 PM . Last Modified: ‎2024-04-03 02:48 AM

In response to DCIM_Support
0 Likes
0
1638
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:00 PM . Last Modified: ‎2024-04-03 02:48 AM

Thanks for the info.

I would be comfortable with manually editing the INI files but then using a different utility to push them out kindof defeats the purpose of having DCE...

Is there any way to download/upload INI files from the StruxureWare server (i.e. FTP)?

(CID:143760158)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:00 PM . Last Modified: ‎2024-04-03 02:47 AM

In response to DCIM_Support
0 Likes
0
1638
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:00 PM . Last Modified: ‎2024-04-03 02:47 AM

Hi Martin,

No, you can't download the configuration file from DCE. What I would suggest is to configure one of the devices the way you want it and then download that file from the device itself using ftp:  get config.ini

I'ts not always the easiest thing to understand but you can take out entire sections or create an INI with just the 1 or 2 sections you want. You could for instance make a text file with the following info and saave it as an INI file and push it to a device:

[NetworkWeb]
Port=80
HTTP=enabled
HTTPSPort=443
HTTPS=disabled
MinimumProtocol=TLS1.1

 

It simply needs the header in brackets  [NetworkWeb] and one or more of the supported entries.

 

K-base FA156117 may tell you more about how to work with the ini files.

 

(CID:143760387)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 07:00 PM . Last Modified: ‎2023-10-22 03:49 AM

0 Likes
0
1638
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 07:00 PM . Last Modified: ‎2023-10-22 03:49 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore