Posted: 2024-02-29 11:32 PM
Hi All,
I wish to remotely Restart a NetBotz 755 via the Web Client however there is no clickable button under the Restart Option. The NetBotz is running on v5.3.5.
I have several NB 755s and its the same across all of them.
See screenshot below:

TIA!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-03-11 02:07 PM
That's due to user privileges. If you log in as superuser the option will not be grayed out.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-03-11 02:07 PM
That's due to user privileges. If you log in as superuser the option will not be grayed out.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-03-11 02:09 PM
you must login as superuser in order for that to work.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-03-12 12:53 AM
Thank you!