Procedure to increase storage for the DCE virtual appliance on VMware

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Procedure to increase storage for the DCE virtual appliance on VMware
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:46 PM . Last Modified: ‎2024-04-08 12:05 AM

0 Likes
5
1345
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:46 PM . Last Modified: ‎2024-04-08 12:05 AM

Procedure to increase storage for the DCE virtual appliance on VMware

In order to increase storage for the DCE virtual appliance on VMware, you must create additional hard disks.

You cannot change the size of an existing hard disk, or remove a hard disk once it has been

created. An error will occur on the primary interface, and the StruxureWare Data Center

Expert virtual appliance will not start.

 

1. Gracefully shut down the virtual appliance.

2. In your virtual server console, select the option to add a hard disk.

3. Choose the hard disk size.

See StruxureWare Data Center Expert virtual server equivalent configurations.

4. Choose thin or thick provisioning.

5. Power on the virtual appliance. StruxureWare Data Center Expert 

 

 

 

 

Changes in the disk space will take effect once the StruxureWare Data Center Expert virtual

appliance has restarted. Do not shut down the virtual appliance while the disk

reconfiguration process is running.

 

The "Storage Settings" display, accessed from the Server Administration Settings option

in the System menu, shows the total storage space available for the virtual appliance, not

the individual hard disks.

I hope it helps. 

Regards,

Bala

(CID:122688329)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:46 PM . Last Modified: ‎2024-04-08 12:05 AM

0 Likes
0
1345
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:46 PM . Last Modified: ‎2024-04-08 12:05 AM

I'm looking to perform an upgrade to 7.3.1 and then up to 7.4.3.

It looks like it is recommended to add a new disk, rather than expanding the 18gb base drive. How much space is recommended when configuring the additional virtual drive for upgrading 2 versions?

 

(CID:126167921)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:46 PM . Last Modified: ‎2024-04-08 12:05 AM

0 Likes
0
1345
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:46 PM . Last Modified: ‎2024-04-08 12:05 AM

Hi Jesse,

I would first suggest you to take the current DCE backup. Therefore, you can restore the DCE in case if something goes wrong. 

And then please check the current storage space under DCE-Administration Settings-Storage

Please check if you have the enough space available.

If possible, please share the screen shot of the current storage. The recommended storage space depends upon the setup such as number of devices, number of alarms, data etc., So it varies as per the requirement of the user. 

You can perform the upgrade as upgrading from 7.3.1 to 7.4.3 may not consume more storage as long as you have enough storage left. You may add additional hard disk to 100 GB which should be fine. 

Regards,

Bala

(CID:126167935)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:46 PM . Last Modified: ‎2024-04-08 12:05 AM

0 Likes
0
1345
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:46 PM . Last Modified: ‎2024-04-08 12:05 AM

snip.jpg

I've uploaded the screenshot as requested.

We definitely do not have an extreme number of devices in our configuration.

Jesse

(CID:126167951)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:47 PM . Last Modified: ‎2024-04-08 12:05 AM

0 Likes
0
1345
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:47 PM . Last Modified: ‎2024-04-08 12:05 AM

I believe you can perform the upgrade activity with the current storage. As mentioned, please take the DCE config and full backup before performing the upgrade. 

(CID:126168105)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:47 PM . Last Modified: ‎2023-10-22 03:39 AM

0 Likes
0
1345
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:47 PM . Last Modified: ‎2023-10-22 03:39 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore