Problems integrating with HPOneview 2.00.02

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Problems integrating with HPOneview 2.00.02
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:19 AM . Last Modified: ‎2024-04-09 12:57 AM

0 Likes
7
946
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:19 AM . Last Modified: ‎2024-04-09 12:57 AM

Problems integrating with HPOneview 2.00.02

Hi Community,

I'm currently onsite with a customer who has carried out an integration with HP Oneview.

The system was version 1.10 but now has been upgraded to 2.00.02.0219211 - since the upgrade DCO cannot communicate with the Oneview system.

The username and password details are the same and all network related hardware has not changed.

Any ideas?

(CID:105466552)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:19 AM . Last Modified: ‎2024-04-09 12:57 AM

0 Likes
0
946
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:19 AM . Last Modified: ‎2024-04-09 12:57 AM

Hi Hiren, We've tested against both 1.10 and 1.20 extensively, but have done only smoke tests for the 2.00 release, which worked fine on when we checked for operability. Last time round, there were some changes in the security code in Oneview. I suspect something similar has happened again. I'll alert my contacts at HPE we have a problem and will see what support I can muster from them. Have you tried deleteing and recreating the external system connection?

(CID:105466557)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:19 AM . Last Modified: ‎2024-04-09 12:57 AM

0 Likes
3
946
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:19 AM . Last Modified: ‎2024-04-09 12:57 AM

Hi Hiren,

I think we have a service patch that -might- resolve this problem - the service pack has been designed and tested with HP OneView 1.20.05. (we have not tested with HP Oneview 2.0..., we don't have that)

If you wish to give it try, then you can download the files from my box soon (I will send you the url by email right away).

Kind regards

(CID:105466559)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:19 AM . Last Modified: ‎2024-04-09 12:57 AM

In response to DCIM_Support
0 Likes
0
946
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:19 AM . Last Modified: ‎2024-04-09 12:57 AM

Hi Hiren, Sharing the info with Community, Many thanks for confirming via direct email that you've gotten the patch installed and working now! Kind regards

(CID:105466719)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:19 AM . Last Modified: ‎2024-04-09 12:57 AM

In response to DCIM_Support
0 Likes
0
946
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:19 AM . Last Modified: ‎2024-04-09 12:57 AM

Jef Faridi Jef, I am also trying to connect to HP OneView 2.0. At the moment it just returns the following message, 'The External System returned an error'. After reading a previous post I was going to apply SP3 to DCO. Is this all that is needed or is there a seperate patch (as you said in your previous answer)?

(CID:105470590)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:19 AM . Last Modified: ‎2024-04-09 12:57 AM

In response to DCIM_Support
0 Likes
0
946
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:19 AM . Last Modified: ‎2024-04-09 12:57 AM

Hi James, You are right. The above mentioned support for HP OneView is included in SP3. Kind regards

(CID:105470594)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:20 AM . Last Modified: ‎2024-04-09 12:57 AM

0 Likes
0
946
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:20 AM . Last Modified: ‎2024-04-09 12:57 AM

Hi all,

A short update to share with you that we/DCO team have recently tested DCO 7.5 SP3 with HP OneView 2.00.02.219211. It's been verified that the integration works fine.

Kind regards

(CID:105471503)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:20 AM . Last Modified: ‎2023-10-31 11:30 PM

0 Likes
0
946
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:20 AM . Last Modified: ‎2023-10-31 11:30 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore