Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Problem with discovering via IPMI

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Problem with discovering via IPMI
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 08:19 AM . Last Modified: ‎2024-04-08 03:55 AM

0 Likes
19
3285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 08:19 AM . Last Modified: ‎2024-04-08 03:55 AM

Problem with discovering via IPMI

Hello,

There are no HP servers discovered when I'm trying to discover them using IPMI.

IPMI over LAN was enabled on iLO and local user with Administrator privileges has been created, but discovered server list in DCO is empty. Alternatively, I tried to use ipmitool on my virtual ITO server, but as far as I know ipmitool doesn't work properly with VM. Could you explain how can I adjust IPMI?

Regards.

 

(CID:110005898)

Labels
  • Labels:
  • Data Center Operation
  • Tags:
  • IT Optimize
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 08:19 AM . Last Modified: ‎2024-04-08 03:54 AM

0 Likes
16
3284
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 08:19 AM . Last Modified: ‎2024-04-08 03:54 AM

Hello. When you say ITO and DCO logs are empty, are you saying they are not being collected or they do not contain any errors? It might be helpful if you could collect ITO log files. Do you know who to do this manually? There are two methods for collecting a customer-support.zip file from an IT Optimize server. Method #1 Using the ITO Lite client. * browse to the ITO server web interface at https://:8090/ * You should see a logon window (see below). Logon as apc/apc * click the system settings button in the top right side of the ITO lite view. * from the system settings popup window make sure the "Support" tab is selected. * Click "Download..."... a save-as dialogue will appear. Could take a minute or two depending on how much log information is present on the ITO server * Click "OK" to save the file and send me the results. Method #2: Using the StruxureWare DC Operation client GUI * Logon to the StruxureWare DCO client GUI. * From the "Help" menu, click "Download log files" * choose the destination for the log files folder and click "OK" * Save the results. This can take several minutes to complete. An output folder will be created with the current date/time as its name. * The files can be large, so if you double-click the server-log.zip file to expand it, you can keep expanding sub-folders server and ito. You'll see a customer-support.zip file for each ITO server attached to the StruxureWare host. I only need the customer-support.zip file from the ITO server, I do not need the entire server-log.zip file. If the server-log.zip file is small enough to email, feel free to send the entire zipped file. IPMI discovery problems are usually centered around a few problems one or two of which you may have already covered in your above posting. * You mentioned you're using an administrator account. I assume you can browse to the ILO and logon with those credentials? * Which make and model is the HP server? * What is the firmware version of the ILO card and how old is it(this info is usually present on the ILO status page when you logon to the card)? ILO firmward should be recent ... if possible a 2015 or newer version. * Does the ILO return a serial number when discovery is attempted? * Could there be firewall rules blocking discovery? Have you used the Intel DCM tool to try to manually discover the ILO? I have attached a procedure to do so ... this is similar to using ipmitool.

(CID:110006091)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 19
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 08:19 AM . Last Modified: ‎2024-04-08 03:54 AM

0 Likes
0
3284
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 08:19 AM . Last Modified: ‎2024-04-08 03:54 AM

p.s. ITO and DCO logs are empty.

(CID:110005903)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 08:19 AM . Last Modified: ‎2024-04-08 03:54 AM

0 Likes
16
3285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 08:19 AM . Last Modified: ‎2024-04-08 03:54 AM

Hello. When you say ITO and DCO logs are empty, are you saying they are not being collected or they do not contain any errors? It might be helpful if you could collect ITO log files. Do you know who to do this manually? There are two methods for collecting a customer-support.zip file from an IT Optimize server. Method #1 Using the ITO Lite client. * browse to the ITO server web interface at https://:8090/ * You should see a logon window (see below). Logon as apc/apc * click the system settings button in the top right side of the ITO lite view. * from the system settings popup window make sure the "Support" tab is selected. * Click "Download..."... a save-as dialogue will appear. Could take a minute or two depending on how much log information is present on the ITO server * Click "OK" to save the file and send me the results. Method #2: Using the StruxureWare DC Operation client GUI * Logon to the StruxureWare DCO client GUI. * From the "Help" menu, click "Download log files" * choose the destination for the log files folder and click "OK" * Save the results. This can take several minutes to complete. An output folder will be created with the current date/time as its name. * The files can be large, so if you double-click the server-log.zip file to expand it, you can keep expanding sub-folders server and ito. You'll see a customer-support.zip file for each ITO server attached to the StruxureWare host. I only need the customer-support.zip file from the ITO server, I do not need the entire server-log.zip file. If the server-log.zip file is small enough to email, feel free to send the entire zipped file. IPMI discovery problems are usually centered around a few problems one or two of which you may have already covered in your above posting. * You mentioned you're using an administrator account. I assume you can browse to the ILO and logon with those credentials? * Which make and model is the HP server? * What is the firmware version of the ILO card and how old is it(this info is usually present on the ILO status page when you logon to the card)? ILO firmward should be recent ... if possible a 2015 or newer version. * Does the ILO return a serial number when discovery is attempted? * Could there be firewall rules blocking discovery? Have you used the Intel DCM tool to try to manually discover the ILO? I have attached a procedure to do so ... this is similar to using ipmitool.

(CID:110006091)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 08:20 AM . Last Modified: ‎2024-04-08 03:54 AM

In response to DCIM_Support
0 Likes
0
3284
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 08:20 AM . Last Modified: ‎2024-04-08 03:54 AM

Hi Greg, Thank you for reply. I found that DCM service has not been installed on server. After installing DCM IPMI works fine, but I have one question about server temperature displaying. As you can see in attached pictures, the temperature displays in DCM but in DCO Server Temperature graph is empty. How can I fix it?

scr1.PNG

scr2.PNG

(CID:110006137)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 08:20 AM . Last Modified: ‎2024-04-08 03:54 AM

In response to DCIM_Support
0 Likes
0
3284
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 08:20 AM . Last Modified: ‎2024-04-08 03:54 AM

Are you referring to the temp info in the tool-tip in when viewing the ITO overlay in DCO? If you switch to the cooling overlay in DCO does the temp appear on the front of the server? Greg

(CID:110006150)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 08:20 AM . Last Modified: ‎2024-04-08 03:54 AM

In response to DCIM_Support
0 Likes
0
3284
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 08:20 AM . Last Modified: ‎2024-04-08 03:54 AM

>>Are you referring to the temp info in the tool-tip in when viewing the ITO overlay in DCO? Yes, I meant tool-tip in the ITO overlay. >>does the temp appear on the front of the server? In the cooling overlay temperature appears on the front of the servers.

(CID:110006169)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 08:20 AM . Last Modified: ‎2024-04-08 03:54 AM

In response to DCIM_Support
0 Likes
0
3285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 08:20 AM . Last Modified: ‎2024-04-08 03:54 AM

Ok. As of today, the temp tool-tip info in the ITO overlay is only filled in by the HP OneView integration. A feature request has been submitted to include the inlet temp data from the Intel/DCM integration as well (which is where the IPMI polling data is coming from). If you have HP's OneView product you could use that tool in-place of using ITO to discover your HP server ILO cards. The ITO licensing is still required to see the cpu and temp data when using OneView to discuss and monitor the HP devices. Greg

(CID:110006183)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 08:20 AM . Last Modified: ‎2024-04-08 03:54 AM

In response to DCIM_Support
0 Likes
0
3285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 08:20 AM . Last Modified: ‎2024-04-08 03:54 AM

Thank you for response Greg, I'll try to use OneView. And last question. When I tried to add one of the servers directly to DCM, I've got following error (in attachment). I couldn't find any information what does this error mean.

error.PNG

(CID:110006308)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 08:20 AM . Last Modified: ‎2024-04-08 03:54 AM

In response to DCIM_Support
0 Likes
0
3285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 08:20 AM . Last Modified: ‎2024-04-08 03:54 AM

Yes, this appears to be a DCM error. Can you share ITO log files?

(CID:110006309)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 08:20 AM . Last Modified: ‎2024-04-08 03:54 AM

In response to DCIM_Support
0 Likes
0
3285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 08:20 AM . Last Modified: ‎2024-04-08 03:54 AM

I attached ITO log below.

CustomerSupport.zip

(CID:110006392)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 08:20 AM . Last Modified: ‎2024-04-08 03:54 AM

In response to DCIM_Support
0 Likes
0
3285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 08:20 AM . Last Modified: ‎2024-04-08 03:54 AM

This node in question is 10.128.216.206? The logs have a number of errors for this asset. Can you tell me more about this asset? Its an ILO? If yes, on which HP server model? Is the firmware on this ILO recent?

(CID:110006439)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 08:20 AM . Last Modified: ‎2024-04-08 03:54 AM

In response to DCIM_Support
0 Likes
0
3285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 08:20 AM . Last Modified: ‎2024-04-08 03:54 AM

>>node in question is 10.128.216.206 >>Its an ILO? Yes. It's BL460c Gen8 (iLO Firmware Version 2.40)

(CID:110006446)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 08:21 AM . Last Modified: ‎2024-04-08 03:54 AM

In response to DCIM_Support
0 Likes
0
3285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 08:21 AM . Last Modified: ‎2024-04-08 03:54 AM

I have reached out to the Intel tech support team for some suggestions regarding next step(s). I should note I also found an advisory posted by HP regarding the ILO firmware on this blade. See here: http://h20565.www2.hpe.com/hpsc/doc/public/display?sp4ts.oid=5219994&docId=emr_na-c03874400&docLocal... HP recommends using a newer firmware release as the bug can cause the ILO card to end up in a failed self-test state. I will respond after I get feedback.

(CID:110006458)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 08:21 AM . Last Modified: ‎2024-04-08 03:54 AM

In response to DCIM_Support
0 Likes
0
3285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 08:21 AM . Last Modified: ‎2024-04-08 03:54 AM

When you discovered the blade using the DCM GUI, was the item actually discovered even with the error, so the asset's details were visible in the bottom of the discovery screen in DCM? It may be necessary to restart the ILO, is that an option if needed? Greg

(CID:110006460)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 08:21 AM . Last Modified: ‎2024-04-08 03:54 AM

In response to DCIM_Support
0 Likes
0
3285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 08:21 AM . Last Modified: ‎2024-04-08 03:54 AM

Thanks a lot for your advice Greg. After upgrading iLO firmware the problem has been solved.

(CID:110006507)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 08:21 AM . Last Modified: ‎2024-04-08 03:54 AM

In response to DCIM_Support
0 Likes
0
3285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 08:21 AM . Last Modified: ‎2024-04-08 03:54 AM

Glad to hear its resolved. It can take a little time for data to make its way from the ILO through DCM and ITO to DCO.

(CID:110006852)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 08:21 AM . Last Modified: ‎2024-04-08 03:54 AM

In response to DCIM_Support
0 Likes
0
3285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 08:21 AM . Last Modified: ‎2024-04-08 03:54 AM

Greg Sterling HP OneView does show the graph however it does not display the temperature figure on the front of the server when in the cooling tab. Also is it possible to have some scaling on the graph?

Graph.JPG

(CID:110007131)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 08:21 AM . Last Modified: ‎2024-04-08 03:54 AM

In response to DCIM_Support
0 Likes
0
3285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 08:21 AM . Last Modified: ‎2024-04-08 03:54 AM

Hello James. Can you send a screenshot regarding the request for scaling so I can better understand what you're looking for? I'm trying to verify your comment regarding lack of temp value on the front of the server when in the cooling overlay. You're referring to an actual rack mounted server, correct? not a blade? If true, I'll log an engineering ticket as we try to be consistent regarding how we present data in the overlays. GregS

(CID:110007147)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 08:21 AM . Last Modified: ‎2024-04-08 03:54 AM

In response to DCIM_Support
0 Likes
0
3285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 08:21 AM . Last Modified: ‎2024-04-08 03:54 AM

Greg Sterling It is for a rack mounted server. Will send you a screenshot for that and the scaling issue. (I have attached a small screenshot to the forum comment)

(CID:110007193)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-03 08:21 AM . Last Modified: ‎2023-10-22 03:38 AM

0 Likes
0
3285
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 08:21 AM . Last Modified: ‎2023-10-22 03:38 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore