Power Capacity And Estimated Load For Multiple Breakers In One Rack

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Power Capacity And Estimated Load For Multiple Breakers In One Rack
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:26 PM . Last Modified: ‎2024-04-09 04:32 AM

0 Likes
8
882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:26 PM . Last Modified: ‎2024-04-09 04:32 AM

Power Capacity And Estimated Load For Multiple Breakers In One Rack

Is there a way to display the capacity limit for a rack which has multiple breakers on either or both the A and B feed?  Currently the tool tip bundles all the A (or B) supplies together into the one graph on the rack. 

 

If you hover over the individual power strip it only displays the live reading and not the estimated load.

Is there anyway to view the estimated load for an individual breaker supplying a rack?  I would envision either four graphs, with the same data as shown at the moment for each on the rack view (if there was two breaks for both A and B) or a grey estimated load on the power strip tool tip.  Then the failover can be calculated depending on which other breaker a device is connected to

(CID:97486035)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:26 PM . Last Modified: ‎2024-04-09 04:32 AM

0 Likes
6
882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:26 PM . Last Modified: ‎2024-04-09 04:32 AM

Hi James,

There is an option to turn on what is known as the Advanced Power tooltip

Power Tool Tip Troubleshooting

This will show the individual phases at rack level. 

/Søren

(CID:97486048)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:27 PM . Last Modified: ‎2024-04-09 04:32 AM

In response to DCIM_Support
0 Likes
0
882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:27 PM . Last Modified: ‎2024-04-09 04:32 AM

Søren,

With the Advanced Power on it still shows similar information as the two breakers are on the same phase.  It still misses the estimated load.

(CID:97486054)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:27 PM . Last Modified: ‎2024-04-09 04:32 AM

In response to DCIM_Support
0 Likes
0
882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:27 PM . Last Modified: ‎2024-04-09 04:32 AM

Hi James, I'm not sure I understand what is meant by two breakers on the same phase. Is the rack supplied with 4 rmpdus each with its own breaker and divided into 2 being A-feed and 2 being B-feed? Currently the option above is what we are displaying by default. Once I fully understand the need a feature request might be needed to see the wanted data in the client. /Søren

(CID:97486165)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:27 PM . Last Modified: ‎2024-04-09 04:32 AM

In response to DCIM_Support
0 Likes
0
882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:27 PM . Last Modified: ‎2024-04-09 04:32 AM

Søren, Apologies for not being clearer. The scenario is as you described, the rack is supplied with 4 rmpdus each with its own breaker and divided into 2 being A-feed and 2 being B-feed

(CID:97486182)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:27 PM . Last Modified: ‎2024-04-09 04:32 AM

In response to DCIM_Support
0 Likes
0
882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:27 PM . Last Modified: ‎2024-04-09 04:32 AM

James Thank you very much for your feedback. As you have discovered it is not currently possible to see the details you require. The good news is that we are reworking the capacity module at the present moment and in version 8.0 we will release an improved power overlay as well as improved tool tips. In your scenario you would still see the A and the B feed on the rack. This is due to space constrains on the rack it self. The tool tip on the rack will contain the same information but with more details - lastly the tool tip on the rack mount PDU's will contain both estimated load as well as measured load broken down per phase. If there is any potential fail over load on the rack PDU it will also be shown. With those changes we aim at being able to provide full insight into how the power is calculated - hopefully this will make it easier for you to understand/troubleshoot power connections. Please let me know if you have additional input - and we will do our best to incorporate it into the new design. /Anders

(CID:97486282)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:27 PM . Last Modified: ‎2024-04-09 04:32 AM

In response to DCIM_Support
0 Likes
0
882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:27 PM . Last Modified: ‎2024-04-09 04:32 AM

Anders Thorbjørn Jensen Thanks for the insight into the future development, the estimated load on each rack mount power strip is a good idea. Two other things I would mention about the power strips is the ability to connect to a specific socket number not just a strip (exact same principle as connecting a cable on two patch panels to a specific port number). If this was available it would remove my second point which is to be only able to connect the number of power cables corresponding to the number of power sockets on the strip. Currently you can have a negative number in the Available Power Outlets field.

(CID:97486359)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:27 PM . Last Modified: ‎2024-04-09 04:32 AM

In response to DCIM_Support
0 Likes
0
882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:27 PM . Last Modified: ‎2024-04-09 04:32 AM

James We are aware of the request to track specific outlets on the rack PDUs. We will get to that as soon as we have reworked the capacity module.

(CID:98304065)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:27 PM . Last Modified: ‎2023-10-31 11:29 PM

0 Likes
0
882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:27 PM . Last Modified: ‎2023-10-31 11:29 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore