Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

PUE showing no data

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • PUE showing no data
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:41 PM . Last Modified: ‎2024-04-08 12:53 AM

0 Likes
8
1195
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:41 PM . Last Modified: ‎2024-04-08 12:53 AM

PUE showing no data

 

I did the configuration and associated the script with the DCE sensors the reading is accurate on the devices but while i'm evaluating the PUE it is showing no data. Jef can u pls help me ?

 

(CID:117999577)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:41 PM . Last Modified: ‎2024-04-08 12:53 AM

0 Likes
4
1195
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:41 PM . Last Modified: ‎2024-04-08 12:53 AM

Hi Waseem,

Currently when PUE showing "No data", that means the energy efficiency calculations have been unsuccessful (usually due to misconfiguration). That's great you already have verified scripts to see if they can be evaluated, however there might be other settings/configurations that might be "incorrect".  As suggested in the following tip: , it would be good idea to start out small and just associate a few devices at a time and evaluate the system often...

You might also want to watch this video tutorial illustrating nicely an EE setup  How to measure the data center energy efficiency

PS. it seems you might be running 8.0, so I would like to recommend upgrading to the latest version (currently 8.1), that contains many enhancements (including the way UI/client should display the script folder(s) only once on screen and not being displayed multiple times).

Kind regards

(CID:117999845)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:41 PM . Last Modified: ‎2024-04-08 12:53 AM

0 Likes
0
1195
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:41 PM . Last Modified: ‎2024-04-08 12:53 AM

This is the script evaluate similarly for all it is accurate but still in when i calculate pue it shows no data.

(CID:117999599)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:41 PM . Last Modified: ‎2024-04-08 12:53 AM

0 Likes
0
1195
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:41 PM . Last Modified: ‎2024-04-08 12:53 AM

Hi Waseem Khan,

thanks for posting. Lets see who can be of assistance here. @community any ideas?

Kind regards Ditte   

(CID:117999656)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:41 PM . Last Modified: ‎2024-04-08 12:53 AM

0 Likes
4
1196
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:41 PM . Last Modified: ‎2024-04-08 12:53 AM

Hi Waseem,

Currently when PUE showing "No data", that means the energy efficiency calculations have been unsuccessful (usually due to misconfiguration). That's great you already have verified scripts to see if they can be evaluated, however there might be other settings/configurations that might be "incorrect".  As suggested in the following tip: , it would be good idea to start out small and just associate a few devices at a time and evaluate the system often...

You might also want to watch this video tutorial illustrating nicely an EE setup  How to measure the data center energy efficiency

PS. it seems you might be running 8.0, so I would like to recommend upgrading to the latest version (currently 8.1), that contains many enhancements (including the way UI/client should display the script folder(s) only once on screen and not being displayed multiple times).

Kind regards

(CID:117999845)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:41 PM . Last Modified: ‎2024-04-08 12:53 AM

In response to DCIM_Support
0 Likes
0
1195
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:41 PM . Last Modified: ‎2024-04-08 12:53 AM

Thank-you Jef Faridi i will try connecting few equipment's only to test.

i have a question is it necessary to define power path in same data center to calculate PUE because in this case i  have not defined the power path i have just created a simple electrical room in which i have placed all the equipment's without connecting them and associated with dce virtual sensors.

Pls suggest ?

(CID:117999872)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:41 PM . Last Modified: ‎2024-04-08 12:52 AM

In response to DCIM_Support
0 Likes
0
1195
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:41 PM . Last Modified: ‎2024-04-08 12:52 AM

Hi Wassem,

It is not necessary to define power path for rack pdu's etc in the data center, but there should be power path between the switchgear and UPS/PDU.

Kind regards

(CID:117999988)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:42 PM . Last Modified: ‎2024-04-08 12:52 AM

In response to DCIM_Support
0 Likes
0
1195
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:42 PM . Last Modified: ‎2024-04-08 12:52 AM

Thank-you Jef Faridi the issue has been solved.

Pue up and running.

 

(CID:118000233)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:42 PM . Last Modified: ‎2024-04-08 12:52 AM

In response to DCIM_Support
0 Likes
0
1195
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:42 PM . Last Modified: ‎2024-04-08 12:52 AM

Hi Wassem,

Excellent, many thanks for the update, appreciated.

Kind regards

(CID:118000240)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:42 PM . Last Modified: ‎2023-10-22 03:32 AM

0 Likes
0
1195
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:42 PM . Last Modified: ‎2023-10-22 03:32 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore