Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

NetBotz 250 : SSH Hostkey and Public/Private keys

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • NetBotz 250 : SSH Hostkey and Public/Private keys
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2020-07-16 09:58 AM

0 Likes
7
5897
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-16 09:58 AM

NetBotz 250 : SSH Hostkey and Public/Private keys

Hello,

 

I am working on security features on the NetBotz 250.

I would like to know if the ssh hostkey, generated by the Security Wizard, is the private key, the public key or both keys of the Rack Monitor NetBotz 250 ?

 

Thank you in advance for the attention you may pay to my question.

 

Raphaêl

Labels
  • Labels:
  • Building Operations
  • Data Center Operation
  • DDF
  • NetBotz
  • Tags:
  • english
  • NetBotz 250
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Shaun
Shaun Leader
Leader

Posted: ‎2020-07-17 04:18 AM

In response to Anonymous user
1 Like
1
5860
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-17 04:18 AM

Hi Raphaël,


The HostKey is the server's (in this case, your 250's) key pair.  When the connection is first established, the server sends its public key to the client.  The client creates a "shared secret", and uses the server's public key to encrypt it, and then returns this to the server.  Now both client & server know this shared secret - the client because it created it, the server because it could use its private key to decrypt it - but for a third-party attacker, neither is true, so it doesn't have the shared secret.

 

The shared secret is then used as the password for a much more efficient cipher (eg AES).

 

For this to work, the client needs to be able to trust that the key it received from the server, really came from the server.  For SSL/TLS, this is done by signing the key using another key the client already knows and trusts (a CA).  This is actually possible in some ssh implementations too, but more typically we just compare the key against a copy we already have.

 

The first time you connect, your client doesn't already have a copy - so you'll be presented with the key's "fingerprint".  This is just a cryptographic hash of the public key, to make this comparison easier for a human to make.  In the web interface of the 250 (Configurating->Network->Console->SSH Host Key), this is shown as an MD5 hash.  Many clients now prefer sha256 by default, but you can usually ask them to show MD5 also in order to make this comparison (eg, for openssh this would be ssh -o FingerprintHash=md5 user@host..).

 

Once you accept that you trust this key, the public key is saved to speed this up in future connections (eg, in openssh this is the known_hosts file; the long string on each line is a public key encoded with base64).  Most implementations store the whole key rather than the fingerprint - it prevents collision attacks, and saves having to hash it every time - at the low cost of using a few more bytes on disk.

 

To bring this back to the 250; if the client connects and receives a key it doesn't trust, and especially so when the key has changed, a well-behaved ssh client will stop and inform you something unusual has happened.  This is the correct behaviour, but can be a real nuisance if you've had to replace or reset the card for perfectly innocent reasons - especially if ssh is being used for automations where this stop isn't immediately visible.  So we provide a mechanism to replace this key - so you can install your own, and if you ever need to reset or replace the card, you can install the same key again to quickly and easily re-establish this trust relationship for all clients.

 

This is all a standard (and mandatory) part of any ssh implementation - but because it's so rarely interacted with, it's easily forgotten.  Most people are used to dealing with their own user ssh keys, and assume that's the keys they're looking at - as Gavan said, at this time we don't support the user-key mechanism.

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Anonymous user
Not applicable

Posted: ‎2020-07-17 12:38 AM

0 Likes
6
5882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-17 12:38 AM

Hi rf2019,

 

It's both, Security Wizard will generate a .P15 file which as far as I know is unique to APC devices. .P15 file can contain just the private key or they can contain both similar to a .PFX file.

 

I assume you mean the GUI version of Security Wizard, if so it will also give you the thumbprint that can be used for host verification to prevent "man-in-the-middle" attacks.

 

-Gavan  

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-07-17 01:33 AM

In response to Anonymous user
0 Likes
5
5880
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-17 01:33 AM

Hi Gavan,

 

Thank you for your reply.

So if I understand correctly, the .p15 file has merged within the public and private ssh keys.

 

Is there any way to send to the Rack Monitor the public and the private ssh keys in different files ?

 

Raphaël

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-07-17 02:00 AM

In response to Anonymous user
0 Likes
4
5875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-17 02:00 AM

Hi rf2019,

 

Can I just clarify, you are talking about the SSH host key and you talking about using public key private key authentication?

 

For an SSH host key there isn't really public and private keys, there is a host key and a thumbprint which can't be separated.

 

The 250 doesn't support public/private key authentication, you need o use password based authentication. 

 

-Gavan

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-07-17 02:21 AM

In response to Anonymous user
0 Likes
3
5873
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-17 02:21 AM

Hi Gavan

 

I think I start to better understand how it works.

But if the Rack Monitor is the SSH server, does the client connecting to it (let's say a PC) will require the hostkey to be stored in its memory, or is the fingerprint alone sufficient enough ?

 

Thank you in advance.

Raphael

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-07-17 02:55 AM . Last Modified: ‎2020-07-17 03:52 AM

In response to Anonymous user
1 Like
0
5871
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-17 02:55 AM . Last Modified: ‎2020-07-17 03:52 AM

I'm not an expert on SSH but it's not like HTTPS.

 

Think of it like a checking the CRC for a file that's been downloaded from the internet. The SSH server assumes that you already know its thumbprint and on connection it expects you or your SSH client to confirm that the provided key matches what you think it should be.

 

The thumbprint is generated by hashing the host key in some way. (I don't know the exact details).

 

-Gavan 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Shaun
Shaun Leader
Leader

Posted: ‎2020-07-17 04:18 AM

In response to Anonymous user
1 Like
1
5861
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-17 04:18 AM

Hi Raphaël,


The HostKey is the server's (in this case, your 250's) key pair.  When the connection is first established, the server sends its public key to the client.  The client creates a "shared secret", and uses the server's public key to encrypt it, and then returns this to the server.  Now both client & server know this shared secret - the client because it created it, the server because it could use its private key to decrypt it - but for a third-party attacker, neither is true, so it doesn't have the shared secret.

 

The shared secret is then used as the password for a much more efficient cipher (eg AES).

 

For this to work, the client needs to be able to trust that the key it received from the server, really came from the server.  For SSL/TLS, this is done by signing the key using another key the client already knows and trusts (a CA).  This is actually possible in some ssh implementations too, but more typically we just compare the key against a copy we already have.

 

The first time you connect, your client doesn't already have a copy - so you'll be presented with the key's "fingerprint".  This is just a cryptographic hash of the public key, to make this comparison easier for a human to make.  In the web interface of the 250 (Configurating->Network->Console->SSH Host Key), this is shown as an MD5 hash.  Many clients now prefer sha256 by default, but you can usually ask them to show MD5 also in order to make this comparison (eg, for openssh this would be ssh -o FingerprintHash=md5 user@host..).

 

Once you accept that you trust this key, the public key is saved to speed this up in future connections (eg, in openssh this is the known_hosts file; the long string on each line is a public key encoded with base64).  Most implementations store the whole key rather than the fingerprint - it prevents collision attacks, and saves having to hash it every time - at the low cost of using a few more bytes on disk.

 

To bring this back to the 250; if the client connects and receives a key it doesn't trust, and especially so when the key has changed, a well-behaved ssh client will stop and inform you something unusual has happened.  This is the correct behaviour, but can be a real nuisance if you've had to replace or reset the card for perfectly innocent reasons - especially if ssh is being used for automations where this stop isn't immediately visible.  So we provide a mechanism to replace this key - so you can install your own, and if you ever need to reset or replace the card, you can install the same key again to quickly and easily re-establish this trust relationship for all clients.

 

This is all a standard (and mandatory) part of any ssh implementation - but because it's so rarely interacted with, it's easily forgotten.  Most people are used to dealing with their own user ssh keys, and assume that's the keys they're looking at - as Gavan said, at this time we don't support the user-key mechanism.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-07-21 04:27 AM

In response to Shaun
0 Likes
0
5833
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-21 04:27 AM

Thank you Shaun for your detailed and precise information.

 

Just another last question.

For what I understood, NetBotz uses the hostkey (mix of public and private key).

However, is it possible to define a public and a private key, generated and defined by a bespoke security key generator, and input them on the NetBotz, so the SSH server on the NetBotz uses such keys ?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore