Posted: 2024-02-01 06:41 AM
we are planning to move one dc.
I have created the new dc with the rack.
now i want to simulate the move.
i copy the asset and paste it into the new dc.
but the properties of the network are lost.
is there a way to copy the asset without losing the properties?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-02-05 05:39 AM
Hello, you are correct, if you copy/paste the items are replicated and connections are lost. Please try using cut and paste instead. Cut and paste should maintain the original asset properties and connections. For example if I right click on a rack in one room, choose cut, then move to another room and paste. The rack, its content, power connections and so on are all kept.
Regards
Greg Sterling
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-02-05 05:39 AM
Hello, you are correct, if you copy/paste the items are replicated and connections are lost. Please try using cut and paste instead. Cut and paste should maintain the original asset properties and connections. For example if I right click on a rack in one room, choose cut, then move to another room and paste. The rack, its content, power connections and so on are all kept.
Regards
Greg Sterling
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.