Thanks, but we have in Argentina 3x380v 50Hz (3 phases and neutral conductor, like Europe), all of ours power panels (or PDU panels) have 380v inputs and mixed between 220v (1 phase and neutral) and 380v (3 phases plus neutral) outputs. we have connected to this power panels´s outputs monitoring PDU (AP8853 220v)
how is the best way to model this panels?
(CID:105458375)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 06:50 PM . Last Modified: 2024-04-09 01:49 AM
Hi
I am not quite sure if I understand you question, so here is a simple answer - please ask again if it does not help:
When connecting a rack PDU like the AP8853 to a power panel (or PDU) you have the choice of using a single phase breaker or 3 phase breaker (provided you have added both types to you genomes), for both breaker type DCO assumes there also is a neutral line - e.g. L1 means L1 to neutral.
If you choose a single phase breaker DCO knows the corresponding phase-to-neutral voltage and is going to use that instead of the 3 phase voltage.
In your case - as long you have defined the output voltage of the power panel to be 380V - you will get 220V on the single phase rack PDU, provided that you have defined 220V as a possible output voltage on that rack PDU.
Kind Regards,
Gert
(CID:105458389)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 06:50 PM . Last Modified: 2023-10-31 11:22 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.