Can the DCE modbus implementation support authentication?
(CID:130680553)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 05:00 PM . Last Modified: 2024-04-05 12:03 AM
Dear Lal,
I agree with Chris. As far as I know, the modbus protocol itself does not support authentication feature as the way SNMP has.
Therefore, authentication is not available in DCE for modbus device communication.
Regards,
Bala
(CID:130681200)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 05:00 PM . Last Modified: 2024-04-05 12:03 AM
Not that i'm aware of.
Also,modbus as a protocol itself does not suppport authentication.
Back to DCE,it only reads device sensor data via modbus tcp,no write /control.
(CID:130680577)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 05:00 PM . Last Modified: 2024-04-05 12:03 AM
Dear Lal,
I agree with Chris. As far as I know, the modbus protocol itself does not support authentication feature as the way SNMP has.
Therefore, authentication is not available in DCE for modbus device communication.
Regards,
Bala
(CID:130681200)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 05:01 PM . Last Modified: 2023-10-22 03:03 AM