Migrate to a virtual machine and additionally update to latest version

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Migrate to a virtual machine and additionally update to latest version
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 07:52 PM . Last Modified: ‎2024-04-04 11:05 PM

0 Likes
4
875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:52 PM . Last Modified: ‎2024-04-04 11:05 PM

Migrate to a virtual machine and additionally update to latest version

On behalf of Juan:


Hello community, this is to consult you on the following point. I currently have an AP9470 physical DCE, with 200 licenses + 25 licenses for a total of 225 activated on 03/20/2013. the version I own is 7.0.0 and I want to make the following improvements. Migrate to a virtual machine and additionally update the version to the latest version 7.5.0, so I require your support to achieve this configuration.

Thank you

(CID:132661211)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 07:52 PM . Last Modified: ‎2024-04-04 11:05 PM

0 Likes
1
875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:52 PM . Last Modified: ‎2024-04-04 11:05 PM

Answer from spezialist:

 

Dear Juan Barrios,

Your task must be completed in several stages.

First you need migrate from phisical to virtual appliance (see for example topic Physical DCE AP9470 to VM ). For this you need purchase the activation key for the virtual appliance (see for example topic Upgrading a StruxureWare Data Center Expert virtual appliance demo version to production).

  1. Make a full backup of your physical DCE apliance AP9470 with ISX Central 7.0.0 software (this is an outdated version, that has already been removed from support). Use for this the Server Backup/Restoreoption, accessed from the Server Administration Settings option in the System menu.
  2. Deploy the demo version of ISX Central 7.0.0 OVA (to download it you must contact local technical support), and configure it using the hardware equivalents for the StruxureWare Data Center Expert Basic, Standard, or Enterprise (for AP9470) server from which you are migrating. The available disk space for the virtual appliance must be greater than the disk space used by the hardware server.
  3. Since your 200-node license is tied to the MAC address of your physical AP9470 server, it will not work on your new virtual appliance because of the changed MAC address. Therefore you must contact local technical support. You'll need to provide them with your old MAC address and potentially the passcodes for the license keys to be transferred. You'll also need to register the new MAC address at https://dcimassets.schneider-electric.com/ hopefully under the same account as the old MAC address.
  4. Perform a restore on the virtual appliance, using the Server Backup/Restore option, accessed from the Server Administration Settings option in the System menu.
  5. Purchase the activation key for the virtual appliance. Then apply the activation key to the virtual appliance.
  6. Apply the new virtual appliance node license keys and application license keys you received from APC Support and restart your virtual appliance. Done!

 Secondly, you need to perform a lengthy upgrade process from an older version of ISX Central 7.0.0 to the latest version of DCE 7.5.0. To do this, you must contact your local Technical Support and verify you have a valid software support contract to receive all the necessary versions DCE-update files for a sequential upgrade using the algorithm:

7.0.0 > 7.2.0 > 7.2.1 > 7.2.2 > 7.2.4 > 7.2.5 > 7.2.6 > 7.2.7 > 7.3.1 > 7.4.3 > 7.5.0

The main thing, do not forget before every upgrade step to make a full backup of your virtual appliance. So you will protect yourself from problems and mistakes in the future.

If you have any further questions, please ask.

With respect.

(CID:132661217)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 07:53 PM . Last Modified: ‎2024-04-04 11:05 PM

In response to DCIM_Support
0 Likes
0
875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:53 PM . Last Modified: ‎2024-04-04 11:05 PM

Add on comment:

Set DCE VM Mac address as static, before switching on the VM.

This is to ensure the DCE VM Mac address does not change when moved, vmotion etc.

 

Could not agree more on the good practice of backup.

Also since they are moving to VM, they can also consider DCE VM snaphot (which is not a backup by itself), and usual VM backup best practices.

(CID:132661233)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 07:53 PM . Last Modified: ‎2024-04-04 11:04 PM

0 Likes
0
875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:53 PM . Last Modified: ‎2024-04-04 11:04 PM

Dear Juan Barrios,

Tell us, please, could you solve your question or not?

With respect.

(CID:132662533)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 07:53 PM . Last Modified: ‎2023-10-22 03:02 AM

0 Likes
0
875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 07:53 PM . Last Modified: ‎2023-10-22 03:02 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore