Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Mapping devices to power outlets on EMA107-10

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Mapping devices to power outlets on EMA107-10
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:06 PM . Last Modified: ‎2024-04-03 11:11 PM

0 Likes
4
1563
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:06 PM . Last Modified: ‎2024-04-03 11:11 PM

Mapping devices to power outlets on EMA107-10

The Eaton EMA107-10 Rack Power distribution allows for managing individual power outlets.  Why can I not map individual machine power supplies to specific ports within DCO?  I want to be able to see power changes on individual outlets as an alarm condition within DCE.

(CID:137732663)

Labels
  • Labels:
  • Data Center Expert
  • Data Center Operation
  • Genome
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:07 PM . Last Modified: ‎2024-04-03 11:11 PM

0 Likes
0
1563
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:07 PM . Last Modified: ‎2024-04-03 11:11 PM

Hi Brady,

I can't speak for the DCO side of things but I'm looking at your DCE comment:

 "I want to be able to see power changes on individual outlets as an alarm condition within DCE."

How are you looking for alarms? Are they alarms already existing on the device? That should nearly be automatic and potentially dependent on the DDF.

Are you looking to create thresholds on the outlets? If DCE can see an outlet status, you can manually create a threshold on that outlet. It would likely be "other state sensor" in thresholds.

If DCE can see the load on that outlet, you can create a manual threshold on the load which would likely be watts or kw. 

Please note that any manual threshold created in DCE is subject to the timing of the polling cycle for that device. DCE will only see a load or state change when the device is polled again after the change. Also note that if you right click a device and view sensors and you don't see these values or states, you will likely not be able to create said thresholds.

 

Steve

 

(CID:137732671)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:07 PM . Last Modified: ‎2024-04-03 11:11 PM

0 Likes
0
1563
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:07 PM . Last Modified: ‎2024-04-03 11:11 PM

Hi Brady

Your last point first, I expect that alarms for changes in individual ports on your rPDU will be a function of the rPDU and therefore DCE, not DCO, and assuming it's SNMP, it may require work to the DDF and some alarm configuration.  As long as the rPDU "exposes" that level of detail, you should be able to see it in DCE.  (no help to you but for APC power rails, DCE also has an outlet control feature)

As far as DCO tracking power supplies to individual power outlets on an rPDU, I believe this is not a feature that exists today.  It's something I've pondered and discussed before and have always arrived at the same conclusion.  Due to possible administrative overhead in medium to large DCs, and the dangers associated with "getting it wrong", that info is better stored on the rPDU itself, and therefore available to DCE.  The External System feature of DCO may make this info available to DCO users via device mouse over (needs confirmation anyone?) or say, by right clicking on rPDU in DCO and launching a webpage of the rPDU that displays this info.   As long as you can craft a URL to take users directly to the power outlets page of the rPDU (assuming the rPDU has a web interface) then you can manually or automatically assign the URL to the rPDU in DCO for a right click launch feature for your DCO users.   At the very least you can launch the rPDU home web page from right click on the device in DCO and have users navigate to the outlets page 

I hope the above helps

Cheers

Ed

(CID:137732669)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:07 PM . Last Modified: ‎2024-04-03 11:11 PM

0 Likes
0
1564
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:07 PM . Last Modified: ‎2024-04-03 11:11 PM

Hi Brady,

I can't speak for the DCO side of things but I'm looking at your DCE comment:

 "I want to be able to see power changes on individual outlets as an alarm condition within DCE."

How are you looking for alarms? Are they alarms already existing on the device? That should nearly be automatic and potentially dependent on the DDF.

Are you looking to create thresholds on the outlets? If DCE can see an outlet status, you can manually create a threshold on that outlet. It would likely be "other state sensor" in thresholds.

If DCE can see the load on that outlet, you can create a manual threshold on the load which would likely be watts or kw. 

Please note that any manual threshold created in DCE is subject to the timing of the polling cycle for that device. DCE will only see a load or state change when the device is polled again after the change. Also note that if you right click a device and view sensors and you don't see these values or states, you will likely not be able to create said thresholds.

 

Steve

 

(CID:137732671)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:07 PM . Last Modified: ‎2024-04-03 11:11 PM

0 Likes
0
1563
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:07 PM . Last Modified: ‎2024-04-03 11:11 PM

Hi Brady,

For the DCO side of the question: "Why can I not map individual machine power supplies to specific ports within DCO?"

Modeling rack pdus on power outlet level is included in the near future plans. 

Kind regards

(CID:137732947)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-05 04:07 PM . Last Modified: ‎2023-10-22 03:01 AM

0 Likes
0
1563
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 04:07 PM . Last Modified: ‎2023-10-22 03:01 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore